Unwanted Heat
For example, if all zones are not calling and then I turn up the basement zone, the basement pipes will get hot (increase > 30+F) and the MBR pipes will slowly creep up maybe 5-6F. As best I can tell by listening with a screwdriver in this case, the MBR pump is not running and the basement pump is.
I believe the thermostat is wired correctly because it will turn on the zone when the setting calls for it. There has been no change to the thermostat wiring in 6 years.
I don’t know when this problem started but I have lived here for 7 years and there have been lots of years when the MBR zone worked correctly. Last year was the first year of service for a new boiler.
My home was built in 1986 and has 6 zones of forced hot water baseboard heating running off a gas-fired Laars Minitherm boiler.
well, how long ago did you have your ONIX tubing installed and how long after that did your system gunked up?.
now that the system is cleaned up youve awoke a sleeping giant0 -
I agree with Jamie Hall. You have a check valve sticking open. it may be a separate valve above the MBR pump or integrated in the pump. The Grundfos UP15-58 has a check valve in the discharge flange. Some Isolation flanges can damage this check valve if the pump is running when it gets closed.0
The 6 pumps are Taco 007-F5. I don't think they have a valve.
Photos show what I think are the check valves. Am I right?
Can a check valve be cleaned or does it just get replaced?
It looks like it would be straightforward to unscrew the valve from the housing. Would the system need to be drained?
Is it time to replace them all?0
You are correct. The actual name of the valves are FlowCheck. designed to open when the circulator operates and prevent reverse flow from other circulator zones if a zone is not operating. This is described on page 9 column 2 of Zoning Made Easy. A text published by ITT the B&G circulator guys. The Ghost Flow that @Jamie Hall is referring to is described starting on page 11 at the bottom of the second column and continues on page 12.
here is a link where you might find the text: http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdf
ALSO the one valve closest to the camera when the picture was taken... may not be all the way closed to Automatic. If partially lifted... that can be the source of gravity or ghost flow. Those valves last forever on most systems, no maintenance required unless they fail...
To be sure: Get the boiler up to temperature with no circulators operating. the pipe on the boiler side of the flow check valve should be hot... the pipe on the other side of the flow check should be much cooler. If any pipes are hot on both sides of the valve ... that valve is not closing completely. If you cant turn the screw down more to stop the flow. Replace it!
@EdTheHeaterMan the check valve is as tight down as it goes. So I guess it is time to replace it. Does that require the system to be drained? If so, I'll wait until spring.
In the mean time, there is a ball valve near the check valve. I've turned this about half off. I think it could reduce the flow and let the MBR cool down more.
Thanks a lot for the booklet - I read what you pointed out and will probably read more.
I wasn't sure how to do the test you proposed. The only way I know to bring the boiler up to temperature is to turn up a thermostat and that starts the circulator.0 -
My cutoff valve adjustment worked and the MBR was pleasantly cool last night.
I am guessing that replacing the check valve will require draining the system and for that reason will wait until the spring.0 -
Yes, replacing the Flo-Check will require draining boiler
To do the test... turn off the boiler and let it cool down for several hours. Set all the thermostats below the room temperature. Turn on the boiler and allow only one zone to operate the boiler (not the problem zone) when the boiler reaches 140° or higher, feel the pipe temperature on both sides of the Flo-Check on the problem zone. (and all the other zones that are not operating). If the pipe is hot on both sides, then the valve is not closed and needs to be replaced. If the valve is holding back the temperature, you have a different problem.
@EdTheHeaterMan Warm day today, good day for boiler testing.
Cooled system down to 64F. Turned on Basement zone. Measured temp on boiler side (BS) and far side (FS) of check valves using laser thermometer.
Boiler at 140F BS/FS temp
Foyer 152/81 FS warm to touch
Bsmt 83/89 FS warm to touch
MBR 120/80 FS slightly warm to touch
Kit 121/88 FS warm to touch
Beds 68/64 FS cool to touch
LivRm 88/66 FS warm to touch
Boiler at 160F BS/FS temp
Foyer 128/106
Bsmt 106/113
MBR 136/80
Kit 115/104
Beds 82/70
LivRm 92/67
Looks to me that there may be three bad check valves: MBR, Foyer, and Kit. I have noticed unwanted heat in MBR (original topic of this post) and also in Foyer. I have not noticed it in the kitchen which is a very large (600 SF) zone that often seems to be working hard to reach temperature.
I'll do a different test to see if the Basement check valve holds back the temperature.
I'm not surprised that half the check valves are faulty. If you look at my earlier posts you will see that the system was cleaned last year and before that the boiler water was black gunk. I don't know how a check valve is constructed but it seems like the kind of thing that could be clogged, either by the original gunk or by something that broke free in the cleaning.
What do you think? Replace 3 valves?0 -
When replacing a check valve does the central portion get swapped out or does the whole "T" have to be soldered in?0
Sorry for the delay in reply, out of town for a couple of days. What circulators are you using? If you have newer Taco 007 there is an IFC version that has a check valve built-in. The insert is available to add to the circulator, part number 006-047RP.
https://www.youtube.com/watch?v=nEC15uplGxY
If you don't have the correct circulator, you should replace the FloCheck valves.
Is this on your system that has the Onix Tubing with all the crud that was cleaned out? If so, The crud may be stuck inside the valve mechanism, and not allowing it to close. New valves will solve the problem.
The Circulators that I see in your post from Nov 2018 "...Replace Onix Tubing..." look like the ones that will accept the 006-047RP check valve. This will be a quick fix for now. Change the brass FloCheck valves next spring and change the circulator locations to Pump Away from the expansion tank on the Supply (HOTTER) side of the boiler. The redesign will help with air elimination, which is a contributing factor in your muddy water problem. Be sure to replace the Inhibitor,
after any repair that requires adding water, to keep the metal oxides from forming again.Edward Young Retired
Thanks @EdTheHeaterMan. I will check model on circulators. Regarding the brass flow check valves - the part looks like a T with a central portion that has a knob. Can the central portion be replaced or does the entire T need to be replaced?0
I don't think replacement parts are readily available. If you can get them apart, just clean them. Nothing magic inside! Page 9 of Zoning Made Easy has a cut-away view of the inside of them. Page 10 has a picture of the B&G version of the brass one you have. I would be ready to replace it when you open them up.
Replacing all your flo-control valves is fine, but maybe overkill? Over time, scale builds up on the internals of the flo-control valves, which interferes with their seating. The best solution is to replace the valves in question. Temporarily, try cycling the manual operator up and down, while tapping on the valve with a plastic-headed mallet. Good luck.1
@Gilmorrie , I’m glad I found my rubber mallet. I tapped, opened, tapped, closed, and repeat. I’ve been running two good zones for an hour and the baseboards are cool in all the problem zones: MBR, Foyer, and Kitchen. THANK YOU!! Problem solved, I think.
@EdTheHeaterMan , What a clever solution to upgrade the pumps with IFC. I called Taco and the casting numbers on my pumps show that they can accept the upgrade. I have Taco 007-F5 and they said the IFC was part # 0010-025RP. Why do you say it is just a quick fix? It looks designed as a long term solution. In any case, I love this solution! But I love @Gilmorrie even better. Yes, this is the same system that had the gunk cleaned out. I think moving my circulators to the supply side would be costly, but I understand that air leads to corrosion.
You all have been a tremendous help. Thank you! Considering that a week ago I had ask what a Flow-Check Valve was, I’m a pretty happy camper and feel tremendously skilled with my rubber mallet.
FYI
Boiler at 170F BS/FS temp after 20 min
Foyer 146/81
MBR 146/92
Kit 147/93
QUICK FIX... meant the faster way to solve the problem. No need to do any soldering or breaking down the piping. It is a permanent solution... (unless you get ghost flow on the supply side.) LOL on the rubber mallet.. that takes a "special scientific skill" to "properly perform percussion" Try saying that 10 times fast
PS I like @Gilmorrie 's solution too!Edward Young Retired
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam