How to connect SR506 to Aquastat L8148A
dagc
dagc Member Posts: 13
I want to connect a Taco SR506 switching relay to a oil fired boiler Well Mclain WGO-3 which has a Honeywell Aquastat L8148A connected to it. How do I connect the SR506 to the aquastat L8148A? Thanks
    HVACNUT Member Posts: 7,452
    If all the circulators are in the 506, then simply run a thermostat wire from XX on the 506 to TT on the aquastat.
    dagc
  • dagc
    It worked, thank you.
    One last question, although everything is working fine and just to be on the safe side. I jumped the T T at the burner, is that right?
  • STEVEusaPA
    edited November 2019
    Usually that's right. When the aquastat closes the relay, power is sent down B1 to fire the burner.
    dagc