How to connect SR506 to Aquastat L8148A

dagc
dagc Member Posts: 13
I want to connect a Taco SR506 switching relay to a oil fired boiler Well Mclain WGO-3 which has a Honeywell Aquastat L8148A connected to it. How do I connect the SR506 to the aquastat L8148A? Thanks

Comments

  • HVACNUT
    HVACNUT Member Posts: 6,242
    If all the circulators are in the 506, then simply run a thermostat wire from XX on the 506 to TT on the aquastat.
    dagc
  • dagc
    dagc Member Posts: 13
    > @HVACNUT said:
    > If all the circulators are in the 506, then simply run a thermostat wire from XX on the 506 to TT on the aquastat.

    One more thing > @HVACNUT said:
    > If all the circulators are in the 506, then simply run a thermostat wire from XX on the 506 to TT on the aquastat.

    It worked, thank you.
    One last question, although everything is working fine and just to be on the safe side. I jumped the T T at the burner, is that right?
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited November 2019
    Usually that's right. When the aquastat closes the relay, power is sent down B1 to fire the burner.