Vacuum breaker
furnacefigher15
Member Posts: 514
I really like using angle pattern check valves as vacuum breakers. Trouble is I cant find a make that lasts more then a year lately. Hoffman and Bell Gossett vacuum breakers dont have the capacity I require, and also dont open at a low enough vacuum level.
What is everyone else using. Ive thought about using a thermostatic radiator trap, but not sure if it will reliably trap steam.
Low pressure steam. Outlet to atmosphere. I use them on boiler water columns and steam headers. Every now and again I get a system with erradic flooding issues thats is a result from vacuum/vapor lock. So I install the check valves, and that resolves my water entrapment issues caused by vacuum.0
Let me rephrase that - outlet of the check valve points to the steam side, so technically inlet is atmospheric0
They probably get around 200 to 225 degrees at peak temperature. Some seats are stainless, some brass, some PTFE. All have been rated for steam service. They have also all been installed within a water seal.
IE - in the horizontal run of a U shaped trap.0 -
Most good vents should open on a vacuum at very low differentials -- unless the steam side pressure is too high (many won't open reliably if they are subject to over 3psi on the steam side). In you application here, perhaps the Barnes & Jones Big Mouth might work quite well.Br. Jamie, osb
I think that big mouth might be exactly what Im looking for.0
I like using checks as vacuum breakers as well. I would buy a 300# Milwaukee seems to be pretty good0
What kind of longevity are you getting?0