Conversion Factors
HeatingHelp
Administrator Posts: 718
great web0
I hope the steam professionals and newbees print this stuff and keep it in file. Years ago I bought a book on conversion formulas that had this data in it. The book cost me 30 dollars. You put a lot of effort in here, so thanks.Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
I still have the Burnham Heating Helper. A pocket sized book that has just about all the info you need. I dont believe they offer it anymore. Probably online.0
btu/hr ~= 500 x gpm x delta t
For extra points, where does the "500" come from?HarlowAshur said:btu/hr ~= 500 x gpm x delta t
Albert Einstein0 -
Pounds per gallon (8.34) X Minutes per hour (60) X specific heat of water (1) = 500.4.
When you get into other fluids you need to be careful. With glycol the 500 goes up a little.
Albert Einstein0 -
I read somewhere that a 1,000 gallons of #2 heating oil had the same amount of BTU's as a cord of mixed hardwoods.0
Since you asked...
It looks lie a cord of would is closer to 160 gallons of oil."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
This keeps me awake at night, the gas meter on the side of the house reads in cubic feet, but the gas company bills me in giga-joules. Why convert for billing?
The electric meter reads in watts, or kilowatts, and they bill me in kilowatts.
Zman I put one too many zeros in my post. I burn 6 or 7 cords of wood to heat this house depending on how cold and long a winter is. when I burned oil a couple of winters I was using around 800 gallons. so the 160 figure is in the ball park. Wood BTU's wood vary depending on the type and variety of wood that is used. I took my number that should have been 100 gallons from some information I had on paper. Looks like that was a little inaccurate.Zman said:Since you asked...
It looks lie a cord of would is closer to 160 gallons of oil.0 -
Wood does vary greatly by species and then also by moisture content. That sheet has some links to the sources so you can dial it in further."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
One pound of oven-dry wood of any hardwood species has an available heat value of about 8,600 Btu. Resinous softwood species, such as shortleaf pine, tend to average slightly higher at 9,050 Btu per oven-dry pound.0