steam boiler control

Tom_40
Tom_40 Member Posts: 9
Does anybody know of a control that can operate a single steam boiler in a building with 12 apartments and has one thermostat. I am looking to modulate operation by the outdoor air temperature

Comments

  • RayWohlfarth
    RayWohlfarth Member Posts: 917
    @Tom_40 I like the Tekmar controls. they are easy to set up and reliable
    Ray Wohlfarth
    Boiler Lessons
  • Jamie Hall
    Jamie Hall Member Posts: 16,528
    Cold you be a little more specific? Are you looking to control cycle timing? How long it is on vs. how long it is off? Presumably independent of the inside thermostat? And, presumably, without overriding the boiler's own pressure controls?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Tom_40
    Tom_40 Member Posts: 9
    The inside thermostat will be abandoned. The boiler operation will be on a 1 hour cycle, with operation time calculated on outside air temperature. The colder is becomes, the longer the on time will be.
  • Steamhead
    Steamhead Member Posts: 14,747
    edited September 2019
    Tekmar 279. Make sure the "steam established" sensor gets put in the right place.
    All Steamed Up, Inc.
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HVACNUT
    HVACNUT Member Posts: 4,074
    Shouldn't there still be a centrally located thermostat or sensor even with ODR on a steamer?
  • KC_Jones
    KC_Jones Member Posts: 4,686
    The way the ecoSteam is set up, the thermostat does call for heat, but is essentially a high limit. I set my thermostat at 72, the ecoSteam at 70. The thermostat usually only stops it when it's above 35-40 or so.

    I don't know how any of the other systems work.

    Before the OP asks, ecoSteam never really made it to market, only a few of us have it and there wasn't enough interest to keep it going. For what I paid it's an awesome system, can't talk price, but it's a lot cheaper than some of the other similar products on the market.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Steamhead
    Steamhead Member Posts: 14,747
    HVACNUT said:

    Shouldn't there still be a centrally located thermostat or sensor even with ODR on a steamer?

    Not necessarily. If you set the 279 up correctly, it can operate solely from outdoor temperature.
    All Steamed Up, Inc.
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    HVACNUT
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 9,625
    Tekmar or Heat Timer. TekMar works well. Heat Timer is more $$$$$
  • Tom_40
    Tom_40 Member Posts: 9
    Ray, Thank you very much. The Tekmar 279 steam control fits my needs perfectly.