Piping size for myson panels
rosy
Member Posts: 9
A mechanical room and control panel are about 12' below grade and three Myson panel radiators (2) 24" x 18" and (1) 32" x 24" ( in three bathrooms, each fed by approximately 20 feet of 1/2 - 02 pex. Supply and return lines for the three radiators will run to a crawlspace and route into a 1" copper manifold with 1/2" balancing valves. The Myson's will have TRV valves.
Myson rates the 24 x 18's at around 3k btus and the 32 x 24 at 4.5k btus.
The question is whether to supply those manifolds with 3/4" supply and return pipes or 1/2"? Pump will be a Grundfos 15/58 3 spd. Seems like 3/4" is the way to go to get enough head to overcome the situation of all 3 activating at the same time. The rise from the manifolds in the crawlspace is 2-3 feet.
Thanks,
Dave
Thanks,
Dave
So, are you saying the total for all three of the 24 x18's is 3k btus or 3k btus for each totaling 9k btus?Bob Boan
No. Two at 3 btuh ea. and one at 4.5 btuh for a total of 10.5 btuh.0
The height makes no difference in a closed loop.
You'd need a minimum of 1" copper to feed the manifolds using a standard 20* delta T.
Bob Boan
1/2 is fine .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38330 -
Sorry, I meant 10.5K btuh.0
FYI -- I have used the Buderus panels w/ bypass on three houses using 1/2 pex. Two houses have third floor ... w/o issue. I think at the time I was told keep it around 12k max BTU per zone w/ 1/2 inch.
These are old school CI Buderus boilers -- panels are the main loop using outdoor reset .. small brute primary pump. All the panels have the Danfoss thermostats.
It's really a great system if you can lay out the panels properly0