System 2000 leaking

Rick_41
Rick_41 Member Posts: 67
edited September 2019 in THE MAIN WALL
OK my unit is a bit over 30 years old but I remember they said at the time that it was a lifetime warranty (less labor) So my oil company (cert EK installer ) said that I need to replace the unit @ around $.

So a rep from Energy Kinetics looked at it and said he wasn't interested in repairing it/replacing it as "something" was left off the boiler when it was installed . (I didn't catch what he said the first time and he seemed to not want to repeat that when I asked,..not sure what he could mean.

I have had it serviced with the "gold plan" each year which was supposed to clean it, check out its functions and set any controls and generally check out the unit. So I'm thinking it should be between the oil co installer and Energy Kinetics.I notice that they still talk on their literature about there lifetime warranty. ...from their site: "If you want lower monthly fuel bills, plus a boiler that lasts and is backed by the industry's best lifetime warranty,...call,.....................

Also at their same site,.."System 2000 boilers installed some 40 years ago still operate at or near their original efficiency. How long will they last? The answer is simple : 40 years and still counting!"

Seems to me I should expect the boiler to last longer?

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    edited September 2019
    Well, 30 years is pretty darn good for any boiler, most would be happy to get 20 in this day and age. I would try and find out what was "left off" the original install. Was the Energy Kenitics "rep" directly from the factory??

    We can't talk price on this forum so please remove the cost
    Erin Holohan Haskell
  • Rick_41
    Rick_41 Member Posts: 67
    Re the price,..I forgot about that,..sorry. Ummm I'm not sure how to remove it though.

  • lchmb
    lchmb Member Posts: 2,997
    another thought, usually the warranty only cover's the HX. Which means all the controls need to be moved over, the burner and everything else.. at 30 years old I would say you made out dam good and look at a new boiler. And yes, I would stay with Energy Kinetics..
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,276
    Rick_41 said:

    Re the price,..I forgot about that,..sorry. Ummm I'm not sure how to remove it though.

    I've removed it. Thanks, Rick.
    President
    HeatingHelp.com
  • When you replace this boiler, make sure the installer sizes the replacement properly, according to the heat loss of the building.
    Try and find out what he thought had been done incorrectly.—NBC
  • HVACNUT
    HVACNUT Member Posts: 5,804
    30 years is pretty good. A new EK Frontier is even better. Front service, better Manager, ECM circulator, plenty of hot water. And clean burning. I believe the EK-1 is now coming with the Carlin EZ-1 burner.
    Intplm.
  • Alan Welch
    Alan Welch Member Posts: 266
    I believe it's called a limited lifetime warranty, after that many years there is probably some credit that can be applied to a new boiler if all conditions are met. It's all in the fine print. If your roof shingles don't last the full 30 years you were promised you wouldn't expect a free roof after 25 years. Energy Kinetics does stand behind their products better than most companies.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    I’m sure Roger or someone from EK will be here to advise you. They are fantastic with customer service.
    Yes limited lifetime warranty, which I’m sure is prorated.
    I’d imagine they would do better for you than any other boiler manufacturer, and would probably want the boiler back if it could provide them any insight to make their product better.
    All of this is assuming the boiler was installed correctly and there aren’t any water quality issues combined with or without a leak somewhere in the system.
    As the others stated, 30 years is a 'win' in my book.
    steve
  • Rick_41
    Rick_41 Member Posts: 67
    well I might agree with a STANDARD boiler getting 30 years is pretty good (however I have properties that are going longer than that still with fairly good efficiency. One that was there since 1972 and was there when I purchased the place. Should be no water quality issues. Low mineral well water.
    I don't see any fine print on the packet that I have hanging up with all the other papers in which it does say lifetime limited warranty, other than saying that its backed by the industries best lifetime warranty.

    Also note:

    At their same site,.."System 2000 boilers installed some 40 years ago still operate at or near their original efficiency. How long will they last? The answer is simple : 40 years and still counting!"

    Seems to me I should expect the boiler to last longer?
  • Rick_41
    Rick_41 Member Posts: 67
    OK,..I found the info on warranty on line,(I don't think it was ever given to me) anyway it says after the 25th year and above 75% of the trade list price. I know we are not supposed to talk money but without talking money prices ,.. what in the heck does that mean?

    And is not the pressure vessel replaceable? Over the years a number of other components have been replaced,.

    Doesn't seem like anyone wants to talk about the missing thing sited in the first conversation now that was said to contribute to its failure,
    I suppose they don't want to get into it with the oil company.

    AND they say under in the warranty sheet,.under EXCEPTIONS AND EXCLUSIONS: The warranty is subject to the condition that the residential boiler must have been installed and serviced in accordance with Energy Kinetics instructions ,..

    and it does not assume any liability of any nature for unsatisfactory performance caused by improper installation.

    But the only ones that can install this unit are certified factory trained people.
    Sound like a bit of a weasel clause to me.



    Mad Dog_2
  • Roger
    Roger Member Posts: 329
    Thank you for your comments, everyone. We certainly will honor any applicable warranty.
    @Rick_41 , please let me know the city and state of your residence so I can gather more information from our Territory Manager, or if you would prefer, message me with location, heating professional name, and serial number details to help me properly review your application.
    Best,
    Roger
    President
    Energy Kinetics, Inc.
    STEVEusaPAErin Holohan HaskellJellismattmia2
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    When the PERSEDENT of a manufacturer posts on this site, that really says something!

    I could repost at least a dozen threads on here which a manufacturer SHOULD have done something, but were silent, if they were even bothered by some little installer's quibbles that their product wasted everyone's money and time.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    RogerMad Dog_2jringel
  • Roger
    Roger Member Posts: 329
    @Rick_41 After visiting your apartment building, your territory manager, Mark, let me know that he has been in touch with your heating professional company who also fully stands behind our products.

    They have what I believe is an appropriate resolution, which also involves modifications to correct some site specific deficiencies.

    Please reach out to them to review next steps and let me know if I can be of further assistance.

    Roger
    President
    Energy Kinetics, Inc.
    JellisMad Dog_2
  • Sal Santamaura
    Sal Santamaura Member Posts: 529

    When the PRESIDENT of a manufacturer posts on this site, that really says something!...

    On the Labor Day weekend, no less!
    RogerRobert O'BrienMad Dog_2Solid_Fuel_Man
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,276
    Now that's customer service! Thanks, @Roger.
    President
    HeatingHelp.com
    Mad Dog_2
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,540
    > @Sal Santamaura said:
    > (Quote)
    > On the Labor Day weekend, no less!

    Indeed!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Rick_41
    Rick_41 Member Posts: 67
    Yes,..I'm very impressed!
    I hope I didn't sound too whiny but it was an expense I wasn't counting on after a number of very high unexpected expenses this year. Generally I have been satisfied and impressed with the oil savings (It replaced GE downdraft boiler that came with the building!) I have convinced 3 other landlords to install EK boilers.
    BTW I Met John Marran at the Chatham Fair in NY's Columbia County. I believe he was just starting his company then. I always remember talking to him as he took the time and explained his boiler. Years later it made me choose his company.
    Erin Holohan HaskellMad Dog_2
  • Roger
    Roger Member Posts: 329
    edited September 2019
    Thank you for your kind words and for recommending Energy Kinetics, @Rick_41. It’s always a pleasure to hear about my father and how so many people remember him helping our industry and our company grow.
    Enjoy the rest of your Labor Day weekend!
    Roger
    President
    Energy Kinetics, Inc.
    Robert O'BrienErin Holohan HaskellRich_49Mad Dog_2
  • Roger
    Roger Member Posts: 329
    Thank you, @Rick_41 . I'm glad everything worked out well, and thank you for your positive comments and recommendation!
    Roger
    President
    Energy Kinetics, Inc.
    Solid_Fuel_ManErin Holohan Haskell
  • HVACNUT
    HVACNUT Member Posts: 5,804
    Not trying to hijack the thread but I just saw a piece in the September/October issue of Indoor Comfort about the fortieth anniversary of Energy Kinetics. Congratulations @Roger !
    RogerErin Holohan Haskell
  • Roger
    Roger Member Posts: 329
    Thank you, @HVACNUT - very nice to reach our 40th, especially with such strong support from all our friends in the industry!
    President
    Energy Kinetics, Inc.
    Erin Holohan Haskell
  • Dogma
    Dogma Member Posts: 1
    HVACNUT said:

    30 years is pretty good. A new EK Frontier is even better. Front service, better Manager, ECM circulator, plenty of hot water. And clean burning. I believe the EK-1 is now coming with the Carlin EZ-1 burner.

    30 YEARS also on a system 2000 that was setup with oil and changed to a gas burner in around 1997. Installed in 1993. Just had first real problem repaired, had the ceramic combustion chamber changed out as the original crumbled not bad for 30 years! Just wish EK would have sold me the part to replace myself! I could have saved a grand.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,831
    You're not going to get any better treatment than that!  I remember seeing them in early P & M ads.  Neato system.  Mad Dog 🐕 
  • JayMcCay
    JayMcCay Member Posts: 32
    Hi Maddog we would want to make sure the equipment is set up properly and running well after changing something that is critical for proper combustion, like the chamber.  It seems the system is running well after 25 years. Please give me a call 908 328-7154

    Jay
    Jay McCay
    National Sales Manager
    Energy Kinetics
    908 328-7154 cell
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,831
    Thanks Jay, but I'm not the guy with the EK!  Mad Dog 🐕 
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    @JayMcCay

    You are looking for @Dogma
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    JayMcCay
  • Steamhead
    Steamhead Member Posts: 16,796
    @Dogma , @JayMcCay is right. Any time a combustion unit is worked on, the burner needs a combustion test and retuning if needed. If the company that replaced the chamber did not do this, call them back and have it done- on their dime.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • JayMcCay
    JayMcCay Member Posts: 32
    Thanks - Maddog & steamhead

    Hi Dogma—We would want to make sure the equipment is set up properly and running well after changing something that is critical for proper combustion, like the chamber. It seems the system is running well after 25 years. Please give me a call 908 328-7154
    Jay McCay
    National Sales Manager
    Energy Kinetics
    908 328-7154 cell