CCB-150 COMBI WALL UNIT
MannyLopes
Member Posts: 4
I have a ccb-150 that ran goo for about 6 months of installation, then errors like A48, then A01 not sure what else codes started left and right, keep on reseting it and now and now it stop producing hot water on demand, meaning I open the hot water valve and nothing happens, but once I unplug it and plug it back ignition comes on and if I open the hot water valve I got continuos hot water, once I shut off the valve and turn it back on ignition does not happen,
getting frustrated to the point of trashing it.
1
Sounds like the system has some installation issues. Was it install by a contractor, if so bring him back. If it was installed by yourself, go through the install manual very carefully making sure all instructions have been followed, with no exceptions. Venting, gas pressures, and combustion analysis all must be perfectly calibrated to have good success with the install.2
The A48 error is Air signal protection activation Fault F05 for 150 seconds See Fault F05.
F05
The air pressure transducer does
not receive a sufficient minimum
value within 25 seconds
Possible causes
Incorrect air pressure transducer wiring Check the wiring
Flue not correctly sized or obstructed Check the length of flue and that it is clean.
replaced the air pressure transducer, ignitor, DHW sensor 1 and delivery sensor because it stopped saying A48 but saying F10 , what mess, then Cleaned the water meter sensor, now it turns on when open the faucet but now says F50.. I forgot to say I changed the board too, I got almost $1500 into this boiler and still got a alarm..
F50
Modulation regulator fault
Wiring disconnected
@MannyLopes Have you contacted Utica Technical Support?0 -
Hello all. I had this boiler installed in 2021 it was great until two months ago now I get the A48 error the contractor came back checked it called tech support and still weren’t able to fix it . He was told to replace the board (I saw that another user did but still having issues). I didn’t because it cost $600 plus shipping. Now the tech is telling him it’s the temperature sensor. I think they don’t know how to fix their own product. I’ll never purchase anything from Utica boilers again0
"Firing the parts cannon at it!" Thats Classic, Jack..thats going in my quiver.. Mad Dog1
- 123 Chimneys & Flues