I am trying to substitute 17' of baseboard with a Pensotti flat panel radiator. Just not sure how to do this without upsetting the balance of split loop system shown in the enclosed diagram.. Any suggestions, thoughts, would be helpful.

Comments

  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    What are your connection sizes for the panel rad?

    Assuming what you have now (piping and fin tube) is all 3/4" copper?

    You may be able to do a venturi T to the new rad.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • ced48
    ced48 Member Posts: 469
    edited August 2019
    Options
    !/2" connection for the radiator, 3/4" fin tube. Penscotti offers a bypass valve, which can be adjusted.
  • hot_rod
    hot_rod Member Posts: 22,141
    Options
    typically no more than 3 panel rads in series, with those bypass H valves Unless is upsize the rads on the tail end of a larger series You can calculate temperature drop thru a series of emitters
    Splitting the loop would avoid an excessive delta
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ced48
    ced48 Member Posts: 469
    edited August 2019
    Options
    Because it would be the first emitter in the series, what would happen if it was piped direct? I am not sure how to figure pressure drop for the unit, so there in lies my confusion.