Help with Piping Pensotti Radiator Diagram Attached

ced48ced48 Posts: 453Member
edited August 13 in THE MAIN WALL
I am trying to substitute 17' of baseboard with a Pensotti flat panel radiator. Just not sure how to do this without upsetting the balance of split loop system shown in the enclosed diagram.. Any suggestions, thoughts, would be helpful.

Comments

  • Solid_Fuel_ManSolid_Fuel_Man Posts: 1,691Member
    What are your connection sizes for the panel rad?

    Assuming what you have now (piping and fin tube) is all 3/4" copper?

    You may be able to do a venturi T to the new rad.
    Serving Northern Maine HVAC, and Controls
  • ced48ced48 Posts: 453Member
    edited August 13
    !/2" connection for the radiator, 3/4" fin tube. Penscotti offers a bypass valve, which can be adjusted.
  • hot_rodhot_rod Posts: 11,849Member
    typically no more than 3 panel rads in series, with those bypass H valves Unless is upsize the rads on the tail end of a larger series You can calculate temperature drop thru a series of emitters
    Splitting the loop would avoid an excessive delta
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
  • ced48ced48 Posts: 453Member
    edited August 14
    Because it would be the first emitter in the series, what would happen if it was piped direct? I am not sure how to figure pressure drop for the unit, so there in lies my confusion.