Should I insulate return piping and cold water lines?

Options
D107
D107 Member Posts: 1,849
edited June 2019 in Gas Heating
Have insulation company coming today to measure for 1.25" steel, .75" copper heating and dhw lines. I'm wondering if I should have them insulate the 3/4" copper return lines from where they enter the boiler room, and cold water domestic lines (for summer sweating?) We have many CI rads and the returns can get pretty cold sometimes, so not sure about insulating that. I guess we should insulate all dhw lines visible in basement boiler room. Need some opinions.

Comments

  • Alan (California Radiant) Forbes
    Options
    Yes, I would insulate all the piping.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab