If our community has helped you, please consider making a contribution to support this website.  Thanks!
Noisy Taco X-Pump Block
                    Member Posts: 4,587
                    We've installed many of these, but this one is particularly noisy.  Has anyone experienced this?
            Hi Alan
 the RMB is equipped with an integral IFC (check valve) that could be chattering because of laminar flow. if you're in outdoor reset mode of operation, injection pump turn down causes minimal flow, and subsequent reduced pressure to hold IFC open.
 as the flow decreases, the check valve could chatter. some people have removed the check, with no detriment to performance if you want to avoid chatter entirely.Joe Mattiello
 Taco Comfort Solutions1
            Hey there, Joe:
 We are in setpoint mode and it's not so much of a chatter than a loud hum. The circulators are quite hot as well. Brand new installation.
 Two btu per sq ft for degree difference for a slab0
            A hum and excessively hot circ could be stuck, or air locked and turning electrical energy to boiling water, or heat. I’d pull them and check that they rotate freelyBob "hot rod" Rohr
 Living the hydronic dream0
            I've had pumps of all brands have the occasional "loud one". Or one which is exceptionally off balance and vibrates.
 Nice thing is you can swap out the cartridge if this is the case. I've grown to really dislike the IFC flow-checks. Seems they all pretty much rattle, and with copper/black pipe it can resonate through a system. I've found the old fashioned iron or bronze flow-checks to be much quieter.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
            In a perfect hydronic world, a check would be 12D from a circulator discharge
 The IFC should “pop” and stay open with 1/2 psi or less. I think very low speed on VS circs may lead to some low delta P conditions, in addition to turbulent conditions at full rpm causing potential noise, sounds like geese eating dominoBob "hot rod" Rohr
 Living the hydronic dream1
            Geese eating domino... I like it!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
            We took the X-Pump Block apart and determined that the system pump was making the loud noise. Pulled the motor off the volute to see what was going on and it all looked fine - no debris. We've ordered a new 008 cartridge to see if that does the trick.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
            I think the piping may need to be reconfigured. From the photo, it appears the 90's are close to the pump. This could cause cavitation.0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 112 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam