vapor stat on a short cycle
nsale
Member Posts: 2
in Gas Heating
Hi, I just switch my honeywell pressuretrol for a Vaporstat. With the Pressuretrol all my radiator were banging now with the vapor stat they are very quiet. The only problem is that the vapor stat is running on a very short cycle. My system is fairly new and the boiler is equipped with a 2 stage gas valve.
Any ideas?
Any ideas?
You are running at a lower pressure now, if the boiler is oversized, or poor venting, or both this would be expected performance. This is why sizing and venting are so important on a steam boiler.0
I had my boiler maintain 1 month ago. The system was fairly balance with just a little bit of banging. The guy put some Steam Boiler Cleaner/Inhibitor and since then a lot of air was going out of the vents and a lot of banging start. All the radiators are tilted on the right position.
so I decided to change my pressuretrol for a vapor stat.0 -
First, get the steam boiler cleaner and inhibitor out of there. You need to drain the boiler and refill with just plain vanilla water. If your water is very acid -- pH less than 6 -- you might want to put a little bit of Steamaster in there. Just a little.
Next, what do you have -- if anything -- for main venting? If the vapourstat shuts off the boiler before some of the radiators have started to get warm, you will need more main venting -- whether the boiler is oversized or not.
Now things get a little more complicated, and you really need to have a low pressure gauge (0 to 3 psi) on there to see what's happening. Is the two stage gas valve connected to operater? If so, it should drop to low fire at slightly less than 8 ounces per square inch -- less if you have a two pipe vapour steam system -- and shut off completely at perhaps 1 to 1.5 psi for a conventional two pipe or one pipe system (vapour systems are a little different). Then, as the pressure drops, the low fire should come back on somewhere between the cutoff and that 8 ounce figure. High fire should come back on -- if the thermostat is still calling -- at perhaps 4 ounces. But, as you can see, you need that low pressure gauge to see what's happening.
And don't even worry about the pressures until you get the venting all nicely done.Br. Jamie, osb
@nsale
What controls your lo-hi fire? Are you able to run the boiler lo-hi-off with the controls you have?
You need at least two controls. 1 runs lo hi fire and one limit to shut you off on high pressure0