Hot Water Trouble
Steam heat is off. Water temp problem persists, heat off or on. Unit is around 17 years old.
Bad aquastat control?
Thanks - Mark
if the boiler is hot to the touch it could be the coil is plugged or the mixing valve has gone bad...0
Probably the mixing valve. When you adjust the aquastat the boiler is responding as it should.
When you run the hot water, check the pipes around the mixing (tempering) valve. Should be cool going into the coil. wicked hot coming out to the valve. If it's that way and cool after the valve, well, it's the valve.0 -
Thanks gents...no mixing valve, got rid of that and use standard valves. The furnace shuts down.0
Are you saying you don't think the boiler is meeting the aquastat setting, or not so much?Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
What temp does the boiler gauge read?
If the boiler is coming up to temp and there is no mixing valve, it sure sounds like the coil is fouled."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
It kinda sounds like it's only firing to a low limit setting? I'd replace the aquastat. If this is a sudden problem where everything was perfect beforehand it has to be something electronic malfunctioning. Aquastat is the likely suspect based on your information. I'd look into a digital replacement, but a mechanical one is perfectly fine.1
I think so...when it is off, it will not come on until I bump up the low level setting, runs a few minuits then shuts off, not restarting. I turn the low level up a bit, it starts, runs a few minuits and shuts off. And keeps on doing this as I turn up the low level a few degrees. It keeps shutting off.SuperTech said:It kinda sounds like it's only firing to a low limit setting? I'd replace the aquastat. If this is a sudden problem where everything was perfect beforehand it has to be something electronic malfunctioning. Aquastat is the likely suspect based on your information. I'd look into a digital replacement, but a mechanical one is perfectly fine.
Thanks.0 -
@MarkH10 Why did you remove the mixing valve?MarkH10 said:Thanks gents...no mixing valve, got rid of that and use standard valves. The furnace shuts down.
While you are working on the boiler, you should install a thermostatic mixing valve. Not a tempering valve, but a thermostatic mixing valve. This will protect you from burns due to hot water settings from the boiler. And it will protect your faucets from prematurely burning out the parts inside that will, and do cause leaks.
Do this to protect yourself and your plumbing system.
"Standard valves," as you mentioned, do not protect.0 -
I have had thermo mixing valves on this system over the years, needing to replace them maybe once every 10 - 12 years. Then, in the last 3 years I had had 4 valves fail. Nothing else in my system is failing or corroding...probably the valves today are not as durable as past. I been using Watts valves.Intplm. said:
I did put in ball valves this time around on the advice of the plumber that last installed the mixing valve. The hot is open and the cold is used to control the temp. Water is staying consistent at 120 - 125 degrees, randomly checked over a two week period. If anything, the hot valve may be subject to wear, time will tell. Water at all facets should be fine at the 120 temp.
Today I swapped out the aquastat, original problem solved.
Thanks for the help guys, I'm impressed at the assistance I received here as newbie.0 -
I believe if you used something other than the Watts valve you wouldn't experience so much trouble. I've always views those valves as low end. I've had better luck with Taco and Honeywell. Caleffi makes some really nice mixing valves.0
@MarkH10SuperTech said:I believe if you used something other than the Watts valve you wouldn't experience so much trouble. I've always views those valves as low end. I've had better luck with Taco and Honeywell. Caleffi makes some really nice mixing valves.
What @SuperTech is referring to when he mentions the "Watts" valve. That Watts valve is what is called a "tempering" valve.
He makes the suggestion as I have,that you need to install a "thermostatic mixing valve" like the brands he mentioned (Taco, Honeywell or Caleffi.)
The Watts burns out prematurely as you have alluded to in one of your earlier posts.
If you do not use a thermostatic mixing valve as suggested, you take the chance of causing high temperature water burns to yourself and others. Not to mention the damage you can cause to the faucets and valves in your home.
I strongly suggest that you put one of those valves in as mentioned !1
- 110 Chimneys & Flues