Gravity System Boiler Replacement
How do you connect PEX to the risers? I assume 3/4" pex --> 1.5" iron risers?0
The manifolds allow isolation of each loop for flushing, filling and purging.jbeck said:@Ironman
What is your method of flushing the radiators and risers? Can it be done while connected to the boiler? (I assume you didnt take each radiator outside and flush with the hose)
I took a sample of my boiler water - when i place a magnet against the water, all the black specs are attracted to the magnet.
Iron oxide particles are normal and actually helpful in protecting the iron surfaces in the system. If that's all you've got, then it doesn't need flushing. If there's sludge, then it needs to be flushed and treated and any leaks repaired.
Bob Boan
That would totally depend upon how the system is piped.jbeck said:@Ironman
I recently replaced a radiator valve - when I stuck my finger inside of the radiator, there was some black gooey stuff. So there's definitely sludge.
What is your method to remove sludge on a working hydronic boiler system?
Bob Boan
As a rule, I don't do combi's.
What are your main reasons not to use combi boilers?
Beautiful install! I'm working on a very similar retrofit of old iron pipes and I'm going with a homerun approach for similar reasons. I'm curious, did you go with 1/2" or 3/4 pex al pex?0
I believe it was 5/8" on that job.Bob Boan
What size pipe is your LLH? Looks like 2".
I like to have two tappings at the top. One for an air vent and another for a sensor. We have been using this one for awhile; very affordable.
(Thank you kcopp)8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
3”.Bob Boan
Alan what brand LLH is the one you have on here? Where do yo get it from?0
Two btu per sq ft for degree difference for a slab0
- 169 Indoor-Air Quality
- 50 Industry Classes