Noise issue w/ Lochinvar boiler
zepfan
Member Posts: 456
in Gas Heating
We are having a noise issue with a Lochinvar boiler model# RBN 180. It is one of three of this same model installed in 2004. The three boilers are piped in parallel. One of the boilers makes a humming noise that is noticable throught out the building only when it is firing. We have disassemble the boiler cleaned the outside of the heat exchanger, soaked the burners in hot water and detergent brushed them out, and then reinstalled them
in the boiler. None of this helped. The noise continues. We took the flue pipe apart, check the chimney for obstructions, and the flue pipe that connects to the boiler. The gas manifold pressure is fine, right at 3.5” All three boiler’s combustion was checked in October but I am thinking that the only other thing that could be causing this noise is either an air/fuel ratio issue, or water flow. The noise is only there when the boiler is firing. If the boiler is up to temperature, with it’s circulator still running the noise stops as soon as the burner goes off. Any assistance would be much appreciated. Thanks to all
The final connection to the boiler is done in csst. The mains are all black pipe with the last 6" connected to the boiler done in csst0
The noise just started. It is the lead boiler of the three, and they do not rotate. The other two don’t make this noise and they have the same csst hookup.0
I would change it to hard pipe. Being first in line to fire he is getting full gas pressure and causing some turbulence in the pipe.
But it is still a WAG at best, worth the effort IMO.
D0 -
if think the noise is being carried by the water pipes, could it be a kettling noise, from the fin tubes being limed up on the inside.??
have you checked the water side of the tubes in the recent past?
i have been involved with some fin tube boilers making noises while burning and it was because the tubes were limed up.0 -
- 123 Chimneys & Flues
