Equivalent replacement radiator
bwroga
Member Posts: 44
One of our radiators just went bad. It was made by the H. B. Smith Company, has 12 sections and is approximately 38"x9"x22". It says "Princess 3" around the inlet pipe. My heating contractor suggested a 4T-25H-14 (U.S. Boiler, 4 column, 25 inch high, 14 section). I want to figure out the EDR of the old radiator, so that I can verify that this is an appropriate replacement. Can someone point me in the right direction on how to do this? I googled "H.B. Smith princess 3" but didn't find anything.
Your answer is in here:
https://heatinghelp.com/store/detail/e-d-r-ratings-for-every-darn-radiator-and-convector-youll-probably-ever-see"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
There is no need to buy a $40 book to measure EDR when you can calculate it...
See:
http://www.smithfieldsupply.com/company_info/forms/radiatorest.pdf
https://www.expressradiant.ca/pdfs/product_classic_sizing_how_to.pdf1 -
@Zman I'm a little hesitant to buy the book, since I'm not sure if I'll use it more than once (hopefully
Using the links from @ImYoungxD the I calculated the EDR as 36 and the radiator my contractor wants to use has an EDR of 28. Am I missing something? Or did he pick the wrong size?
https://files.gitshare.io/link/rBDNg1g1CSM/Radiator-Baseboard Product Data Sheet.pdf
Those Smith column rads had higher ratings than the standard type. That one's at least 42 square feet. If they use the 6-tube rather than the 4-tube radiator, it'll be much closer.
Oh, and the newer radiators have shorter legs than that Smith- you'll need pedestals to bring it up to the proper height, or you'll need to shorten the pipe coming out of the floor.All Steamed Up, Inc.
Consulting2 -
I was talking to someone through private message (who I am grateful to for the help he gave), and he told me that that the "Every Darn Radiator" book has listings for H.B. Smith 3 column Princess Radiators at 19 and 25 inches high, and that the heights in the table exclude the legs, so mine was 19 inch.
Then I found a copy of a 1920 H.B. Smith Catalog online that does list 22 inch high radiators in addition to 19 and 25, so I just wanted to confirm:
Are the heights in the tables from bottom of leg to top of the radiator, or do they exclude the leg? And do the EDR's in these tables apply to all 3 column princess radiators made by H.B. Smith? My radiator looks a little different from the ones illustrated in the catalog. The house was built in 1916, but I'm not sure if these are the original radiators or not.
And...should I even be basing the size of the new radiator on the old, or should I base it off the results of a BTU calculator?0
I believe the published radiator heights are from the floor to the top of the radiator. You don't need to use a radiator with the same dimensions as long as the EDR is close. I would try to match the EDR rather than the room heat loss, that will keep that room in balance with the other radiators in the house.0
Use the old radiator as the basis for sizing the new.bwroga said:And...should I even be basing the size of the new radiator on the old, or should I base it off the results of a BTU calculator?
Or, alternatively, you could calculate the heat loss of each room, and the heat input into each room from their respective radiators. Using these figures, calculate a ratio of room heat gain vs. room heat loss for each room, and then select a new radiator that has a similar ratio.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0
- 50 Industry Classes