Hutchison System
Dan Foley
Member Posts: 1,268
I have worked on dozens of Hutchison Vapor Systems over the years. They were prevalent here in the DC metro area.
This is the first one I have seen with the receiver still in place. It is piped wrong (copper). It is also too low. It should be at the water line according to old drawings.
I do not know the inner workings of this receiver but I imagine it operates more like a differential loop than an alternating receiver. Maybe Frank can dig into his library for more info?
This one is located in downtown Herndon, VA. It is not our job. I am helping a contractor friend who is replacing the boiler.
- DF
- DF
Here is the old stub where the dry return vented into the chimney.0
According to Mike's link, that receiver was part of the damper-regulating mechanism.All Steamed Up, Inc.
Consulting-1 -
Does look like it -- a number of vapour systems (Hoffman Equipped did, for instance) either had integral damper controls, or could add them. Early modulating boilers...Br. Jamie, osb