Second Radiator on Home Run Circuit?
OaklandNS
Member Posts: 56
After using my system for a couple of days, I think I've undersized the emitters in one of my rooms. All the circuits are getting plenty of flow, and after running some additional heat loss calculations I think the room just loses more heat than the emitter can provide.
I have two home runs in the room, each feeding a radiator that is rated to put out 3,480 btus at 140* water temp. I would like to add a second radiator to one of the home runs that is rated for 3,120 btus at the same temp.
The current piping is 1/2" fostapex to each home run. The 1/2" should have no problem carrying the btus at a 20* delta t (each radiator needs only about 1/3 a gallon/minute of flow to meet the btu demand). My question is the best way to pipe in the new radiator:
Thanks for your thoughts in advance.
- Pipe both radiators in series with a single TRV controlling flow to both radiators based on the temperature of the room where they are located.
- Pipe both radiators in reverse return configuration with 1/2" legs from the 1/2" mains supplying and returning to each radiator, with each radiator controlled by a dedicated TRV.
- Pipe both radiators in direct return configuration with 1/2" legs from the 1/2" mains supplying and returning to each radiator, with each radiator controlled by a dedicated TRV.
- Add a new home run.
I'd pick your parallel reverse return -- your option 2.Br. Jamie, osb
Thanks Jamie---if that will work, that's a preferred option.
Pipe in series with a single trv, or add new home run if manifold has the space. You didn’t say how short you were in emitter, only how much you were adding. However can’t be much, and the additional headloss of series piping won’t diminish returns that much. 1/2” will carry 15k. The trv only knows proportional demand, and both rads will get the flow.
Cheapest, and will be effective.0 -
Thanks Gordy---the current radiator is rated for 3,5000 btus at my target temp of 140*. The one I want to add is 3,130 btus. So the 1/2" line will be carrying 6,630 total. Well under 15,000. My calculation is not as short as it sounds because there's another radiator in the same large room on a different home run that supplies another 3,500 btus.
Kcopp---I thought about that but there are already holes drilled into the floor for the existing radiator (and I can't use one of the same length due to wall space constraints), not sure if I can return the already-installed radiator, and adding another will put heat on 3/4 walls in the room which I hope will increase overall comfort.
I can't decide if it's a bummer I need to add this radiator because all the other rooms are super comfortable, or if I should count myself lucky that this is the only problem (so far) on my first go around on something like this.
Thanks for all your responses!
Nathan0 -
Have you tried raising your water temps first? If everything has trvs then doing so shouldn’t effect the other rooms.
If you are using a mod/con you could try bumping up in 10degree increments see if it helps.0 -
I did raise water temp to 160 and it's still losing heat overnight.
There's still a bit of guessing because we intend to insulate the attic to at least R-30 (currently uninsulated) and the floor will be insulated as well. But redoing my heat calculations suggest that even after we insulate, I will still need the extra btus. Since the floor joists are open, it makes sense to me to add the additional radiator to ensure everything works well and I can get the emitters sized for a 140* design temperature once we have all the insulation installed.0