burnham IN-6 boiler
keith_27
keith_27 Member Posts: 64
Boiler that was installed some time in 1995 has a honeywell guard ring lwco RA 700. Probe has been serviced over the years but it has acted up a couple times this year. The guard ring is no longer made what would take the place of this module.
  • keith_27
    strictly steam
  • Fred
    Fred Member Posts: 8,542
    Replace it with a Safegard LWCO. They are very good and reliable. Stay away from the Cyclegard, which shuts the boiler down at various intervals to check the water level.
    Ironman
  • keith_27
    thanks fred