90+ Gas Furnace Misfiring (flames sputtering)
csp02
Member Posts: 3
in Gas Heating
What would cause a 90% gas furnace to misfire? As soon as the burners ignite the flame “sputters” (misfire), blower is not running.
A number of things;
dirty burners
gas pressure not right
inducer fan
cracked heat exchanger
probably more
What does the flame do when the blower comes on?
The burners don’t stay on long enough, so the blower doesn’t have a chance to come on0
Does this have a Honeywell Smart Valve on it?
Picture of gas valve would0 -
I found the problem. Water in the pressure switch hose, which was caused by a clogged drain line. Thanks for the help0
Glad you found it, just good ole annual maintenance. Grab the owners manual and you will find more to do. Or even better call a tech and have them go over it, they will check all of that and more, but mostly determine if it truly is operating safely.0
My self ingniting gas furnace flames stays burning when the flame inspection cover is off.but when you put the cover back on,the flames go out.could it be the ingniting rod?it seems it's starving for air when the cover is on,but thrives without it.it ran good for a month.and then this happens.thanks0
Thanks.i haven't figured out how to start my own post.0
You use the orange "New Discussion" tab on the upper right.
With your new post, pictures would be helpful. It sounds like you have a sealed combustion unit? I would first check for blockage in the combustion air piping."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -