90+ Gas Furnace Misfiring (flames sputtering)
csp02
csp02 Member Posts: 3
What would cause a 90% gas furnace to misfire? As soon as the burners ignite the flame “sputters” (misfire), blower is not running.
  • JUGHNE
    JUGHNE Member Posts: 11,549
    A number of things;
    dirty burners
    gas pressure not right
    inducer fan
    cracked heat exchanger
    probably more
    What does the flame do when the blower comes on?
  • csp02
    The burners don’t stay on long enough, so the blower doesn’t have a chance to come on
  • JUGHNE
    Does this have a Honeywell Smart Valve on it?
    Picture of gas valve would
  • csp02
    I found the problem. Water in the pressure switch hose, which was caused by a clogged drain line. Thanks for the help
  • DZoro
    DZoro Member Posts: 1,048
    Glad you found it, just good ole annual maintenance. Grab the owners manual and you will find more to do. Or even better call a tech and have them go over it, they will check all of that and more, but mostly determine if it truly is operating safely. :)
  • jgodina
    jgodina Member Posts: 7
    My self ingniting gas furnace flames stays burning when the flame inspection cover is off.but when you put the cover back on,the flames go out.could it be the ingniting rod?it seems it's starving for air when the cover is on,but thrives without it.it ran good for a month.and then this happens.thanks
  • Zman
    Zman Member Posts: 7,609
    @jgodina
    You will get better results if you start a new post rather than piggybacking off an unrelated one.
    Albert Einstein
    jgodina
  • jgodina
    Thanks.i haven't figured out how to start my own post.
  • Zman
    You use the orange "New Discussion" tab on the upper right.
    With your new post, pictures would be helpful. It sounds like you have a sealed combustion unit? I would first check for blockage in the combustion air piping.
    Albert Einstein
  • JUGHNE
    Z-man, he did re-post his own.
    Cleaned air/vent hoses to pressure switch.
    Zman