Question
347 Member Posts: 149
Happy Holidays to all,
I'm installing a standard cast iron boiler with an indirect water heater, three high temp baseboard zones and adding two radiant heat zones (14k heat loss on both). I would like to do primary secondary piping to reduce the possibility of condensation when the radiant zones are calling.
I can't remember if I should install the piping for the indirect before (one tee before and one after) the closely spaced tees or in the secondary part of the piping. If before the secondary manifold the return tee will be installed the at the boiler return before the circulator for the primary loop.
Thank for the help.
Michael
  • Before
  • Gordy
    Gordy Member Posts: 9,546
    Since you will be adding radiant.
  • 347
    I was thinking something like this, except I'll have the high temp zones after the mixing assembly along with the radiant
  • STEVEusaPA
    You probably want high temp before mixing station, and a few well placed flow checks.
    Gordy
  • Gordy
    edited December 2018
    Yes highest temp zone first.
  • 347
    Yes, I was doing that. Just wanted to double check about keeping higher water Temps on the return.
  • Does it matter if you have DHW priority?
  • Gordy
    No, just the radiant.