Question
347
Member Posts: 143
Happy Holidays to all,
I'm installing a standard cast iron boiler with an indirect water heater, three high temp baseboard zones and adding two radiant heat zones (14k heat loss on both). I would like to do primary secondary piping to reduce the possibility of condensation when the radiant zones are calling.
I can't remember if I should install the piping for the indirect before (one tee before and one after) the closely spaced tees or in the secondary part of the piping. If before the secondary manifold the return tee will be installed the at the boiler return before the circulator for the primary loop.
Thank for the help.
Michael
I'm installing a standard cast iron boiler with an indirect water heater, three high temp baseboard zones and adding two radiant heat zones (14k heat loss on both). I would like to do primary secondary piping to reduce the possibility of condensation when the radiant zones are calling.
I can't remember if I should install the piping for the indirect before (one tee before and one after) the closely spaced tees or in the secondary part of the piping. If before the secondary manifold the return tee will be installed the at the boiler return before the circulator for the primary loop.
Thank for the help.
Michael
0
Comments
-
Before
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Since you will be adding radiant.0 -
I was thinking something like this, except I'll have the high temp zones after the mixing assembly along with the radiant
0 -
-
Yes highest temp zone first.0
-
Yes, I was doing that. Just wanted to double check about keeping higher water Temps on the return.0
-
Does it matter if you have DHW priority?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
No, just the radiant.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements