ESBE valve + converted gravity question
I am adding a bypass to my gravity converted system that came with my house. It's already 25 years old but I'm trying to keep the boiler and my 4-year-old chimney liner as happy as possible.
Was going to do a simple bypass but I got a great deal on an ESBE valve body. The piping diagram, though, looks like I need to have 2 circulators and pump it P/S in order to use on converted gravity. Am I reading this right? The ESBE instructions are hardly comprehensive.
I do worry that if I added the ESBE without P/S that the flow could be so slow through the old gravity pipes that the 3rd floor never gets warm before the thermostat on the 1st floor stops calling.
Am I overthinking this?
  • Zman
    Zman Member Posts: 7,611
    You need a circ on the boiler side and a circ on the system side. The drawing has a 3rd one which is unnecessary. The primary/secondary should be tied together with closely spaced tee's or a hydraulic separator.
    Albert Einstein
  • Bill_17
    Bill_17 Member Posts: 73
    Zman is correct. The ESBE diagram's 3rd circulator is shown with a dotted line around it. The full document indicates that is an alternate, but less desirable, location as compared to being installed on the outlet of the boiler.
  • Bill_17
    See attached ESBE diagram
    hot_rod Member Posts: 26,587
    you would need to analyze the circuit. It’s possible a dongle circulator could be adequate for the boiler glue and distribution, on a direct, non primary secondary piping. There are loading units that are a pump and valve in one assembly. Commonly used on wood fired boilers