Grundfos Magna 3

kcopp
Member Posts: 3,669
I have a customer that has a magna 3 Delta p circulator in his system.
It has been intermittently having issues where the sensor apparently is bad.
I have the sensor but cant find any info available as to if it is a wet tapping that it fits into or a dry one.
thanks
It has been intermittently having issues where the sensor apparently is bad.
I have the sensor but cant find any info available as to if it is a wet tapping that it fits into or a dry one.
thanks
0
Comments
-
-
FYI... Its wet.
Pulled it out and got a squirt.
oh well.
I know now.
0 -
Sorry I missed this. FYI the sensors can get dirty in extreme conditions, they are very easy to wipe clean if necessary.0
-
thanks.
The system is a good sized one.
Im sure a good flush w/ some Fernox would be a good idea.... and some inhibitor after.