Primary secoundary
Other than the Tee being a little close to the Ell, what's wrong with it?Bob Boan
If there is a pump in the boiler yes. Can.t see it working otherwise.0
Bob Boan
I don't like the manifold that navian has, I also don't like the webstone service valves. id rather install a brass tee off the unit then a nipple then a shut off for flushing the unit. if I wanted I could add a union. then make it a 1 1/4 off the shut off , that's what navien manifolds do.
Really shouldn't need flush valves on the heating side of the boiler? Although that valve does make the transition from boiler to copper. A nut and tailpiece can get you to 3/4 or 1" copper with a union.
Try to keep a bit more distance between the tee and any ells or other fittings.Bob "hot rod" Rohr
hot rod there 1 inch nipples coming out of machine, I wanted to go to 1 1/40
Why 1 1/4"?... seems overkill0
just from my understanding anything over 100,000 btu require 10 gpm , 10 gpm at 2 - 4 feet per second is boarderline 1 inch but 1 1/4 will do. the navien 240 is 120,000 BTU on heating side0
With modulation and the Tee's, you'll probably never see all the BTU's going through the secondary manifolds.0
If the boiler connection is 1”.0
That 120,000 can be a misleading number. You'll get that when you have a 50* delta T between the boiler and the system (think radiant slab), but not with high temp emitters (baseboards). The onboard circulator is only good for about 5 gpm.Snowmelt said:just from my understanding anything over 100,000 btu require 10 gpm , 10 gpm at 2 - 4 feet per second is boarderline 1 inch but 1 1/4 will do. the navien 240 is 120,000 BTU on heating side
Always size piping off of gpm, not btus. The btus, when plugged in to the universal hydronics formula, will tell you how many gpm is required. In this case, that's already been determined by the circ that comes on the boiler.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
your right Gordy they are one inch, I do want to educate myself so I am going to ask, even though its 1 inch and I am pretty sure the heat exchanger on the navien combo has a high head pressure with that statement. I am going to say that the internal pump doesn't have a lot of GPM I am thinking 3 - 4, if I increase the pipe diameter I think I can squeeze 6 GPM out of the machine.0
iron man, thats why I want to increase the pipe size0
I actually seen it work , I replaced about 6 foot of 3/4 pipe with 1 inch and I gained 3/4 of a GPM every little bit counts0
- 120 Geothermal