Options
steamfitter
Member Posts: 156
I am checking out an installation of 2 lochinvar power-fin condensing boilers in a boiler room on the roof of a 2 story building. They have relief valves set at 50 psi. I'm wondering why they're not 30 psi. Thoughts?
0
Comments
-
Commercial boilers? What does the nameplate say?
Did the relief valves come with the boilers?0 -
50 lb. relief valves are the standard relief valve that comes with all current Power Fin boilers.0
-
So the 50 lb relief valves are standard with Powerfin boilers?
I'm guessing it allows for that boiler to be used in the basement of a building that requires the PRV to be set at a pressure higher than 12psi (ex: 30 psi) due to the height of the system.
Question: If you have a 2 story building and the boiler is on the roof, and you only need 12 psi on the PRV and Expansion Tank, is it a waste of money to buy and install 30 psi relief valves?
If a problem occurs down the road and the pressure climbs to 30 psi, a leaking relief valve would alert maintenance before it gets to 50 psi. Does that even matter?0 -
My state boiler inspector (CO) requires an ASME rated expansion tank to be installed on any boiler that has a relief valve rated over 30 psi. Might be worth asking your AHJ to check and see. ASME tanks are not cheap at all.....0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements