Lochinvar Power-fin relief valve setting
steamfitter
Member Posts: 156
I am checking out an installation of 2 lochinvar power-fin condensing boilers in a boiler room on the roof of a 2 story building. They have relief valves set at 50 psi. I'm wondering why they're not 30 psi. Thoughts?
0
Comments
-
Commercial boilers? What does the nameplate say?
Did the relief valves come with the boilers?0 -
50 lb. relief valves are the standard relief valve that comes with all current Power Fin boilers.0
-
So the 50 lb relief valves are standard with Powerfin boilers?
I'm guessing it allows for that boiler to be used in the basement of a building that requires the PRV to be set at a pressure higher than 12psi (ex: 30 psi) due to the height of the system.
Question: If you have a 2 story building and the boiler is on the roof, and you only need 12 psi on the PRV and Expansion Tank, is it a waste of money to buy and install 30 psi relief valves?
If a problem occurs down the road and the pressure climbs to 30 psi, a leaking relief valve would alert maintenance before it gets to 50 psi. Does that even matter?0 -
My state boiler inspector (CO) requires an ASME rated expansion tank to be installed on any boiler that has a relief valve rated over 30 psi. Might be worth asking your AHJ to check and see. ASME tanks are not cheap at all.....0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements