Hi All. Need a little help.
Browsed around and can't seem to find an answer on the forum so I'm reaching out for some assistance.
I have a single pipe steam system where the boiler is overflowing. I have an automatic water feeder.
When the boiler is sitting idle the water level is holding steady at about 3" down from the top of the sight glass. It will remain this way indefinitely. When there is a call for heat and the boiler fires up it usually maintains the correct level for 24-36hrs of normal cycling on and off. Around 48hrs of operation I notice the water level is over the top of the sight glass. I blow down approx 3 gallons of water to get the water level to where its supposed to be and the process begins again.
I guess my question is if the boiler is holding level while idle, why is it overflowing when under operation?
Is it a problem with my feeder?
Is there a faulty steam vent somewhere?
Am I getting too much condensate trapped up in the system?
Is my return possibly clogged or restricted slowing the return of condensate? Causing the water feeder to activate, then when the system cools the slow return is causing the problem as the water returns to the boiler?
I need some help diagnosing the issue and any help would be greatly appreciated.
Thanks in advance
Mark
    Steamhead Posts: 18,834
    Could be the return, bad low-water cutoff, etc. Where are you located?
  • NY
  • Snowmelt
    Snowmelt Posts: 1,454
    city , up sate or staton island
    HVACNUT Posts: 7,656
    Seems like a partially blocked return.
    Feeder gets energized. Fills the boiler, then later the condensate makes it's way back.
    What model feeder? You might be able to adjust the delay.
    Fixing the return is better if that's the issue, but adjusting the feeder can help.
  • Ironman
    Ironman Posts: 7,942
    You could try closing the valve to the auto feeder. Then, if the water level goes down and slowly rises, you probably have a clogged return. If not, the feeder could be bad. The down side to trying this is that the LWCO is gonna turn the boiler off as long as the water level is low.
    Check the contractor locator above to see if there’s a steam pro near you.
    Bob Boan
  • Another possibility is if your using this boiler for hot water the tankless coil or indirect may have a pin hole leak.