Bad mixing valve
Snowmelt
Member Posts: 1,454
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/CashAcme-24514-ProductOverview.pdf
Ever have this mixing valve go bad on you?
Bad as in? They tend to lime or scale up easily, all brands do. You need a 20 or more ∆ between hot in and mixed out for them to be accurate. A min. 1 gpm also.
That 20 gpm is BS! try shoving 20 gpm thru an opening the size of a pea. Sure it's possible but look at the pressure drop, what pump would you use for 45 pressure drop?Bob "hot rod" Rohr
It’s only been a month I have the mix at factory setting which was about 120 , the boiler is set at 180, it was nearly Luke warm temperature. I turned it all the way up and still it’s just above Luke warm but not even close to hot.0
did it work when you first installed it, or not ever?Bob "hot rod" Rohr
Had to work, it was hot to touch where I could only hold it for 5 secounds, now it’s Luke warm.0
Did you try turning the knob all the way open and close to see if it frees up a stuck spool?Snowmelt said:Had to work, it was hot to touch where I could only hold it for 5 secounds, now it’s Luke warm.
You are sure you have flow going thru, no air lock that could be causing little or no flow?
Circulator is pumping away from the "H" port?
Are you pumping away from the Mixed port?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
its defiantly stuck closed. I felt the pipe this morning, it may be air bound I will try bleeding the air today. it was working just last week were my wife could feel the floor was warm. the floor didn't feel warm Friday night so Saturday I looked at the valve, it wasn't getting warm.
of course im pumping away from the mix valve, im not a rookie.
im leaning towards air or bad mix0 -
very simple innards, but it doesn't take much to gum them up.
This spool was in a domestic water valve that the water flowing thru started to dissolve the peroxide cured EPDM o-rings that Caleffi uses, a very chemical resistant o-ring design.
Chemicals added to the public water must have been fairly aggressive. Wonder what those chemicals do to human innards
I have seen grit get in there and mess all kinds of things up.
Pull it out and flush the lines as best you can.
May be best to install new valve instead of fixing what you have.0 -
In a bind you can actually remove the guts from a thermostatic valve and move some heat. If there are valves around it you can manually balance it, but it will not change as S&R changes, it's now a dumb valve
You might be amazed how much more flow you move when the guts are taken out. Thermostatic are very flow restrictive devices.
3- 5 GPM reasonably without throwing some serious pump energy at 'em.Bob "hot rod" Rohr
Not understanding how Cv works in a valve like that is probably why so many radiant systems slip behind as you approach design conditions.
You will often see 2 or 3 circulators connected to 3 Cv thermostatic valve!
If this attaches it is a handy spreadsheet to help understand the effect of CV. Used for design or troubleshooting.
It applies to ANY valve, zone, ball, balance.Bob "hot rod" Rohr
Living the hydronic dream1 -
It can take a lot longer than one would think to get a good clean purge, you can spend 5 minutes or more on a single loop getting then to run clear. Good that you got it going.Snowmelt said:Hot rod, it was air in the line. I came home from work, I bleed it out, ( 3 five gallon buckets, then the line became hot.
yea my wife was complaining her feet were cold. lol
hey, were you in NJ a few weeks ago? did a class on your material. john serlerno was the rep?0 -
Hey @Snowmelt should you need to change it I’d recommend the caleffi version. Has a temperature gauge to see what the outlet temp is. Pretty nice valve.0
- 120 Geothermal