steam pressure
Options
Snowmelt
Member Posts: 1,416
towards the end of the summer I installed a union steam boiler, I never looked at the pressure troll, customer called me up said pipes where banging and water spitting out. I went over there the pressure troll was maxed out. the question is did he home owner touch it, was it set like that from factory or was that just a fluke. I put it down to the factory minimum with 1 .5 differential and waited an hour, everything was fine after that? Again was that odd or did someone touch it?
0
Comments
-
It's been my experience that the factory shipping setting is set at maximum. I often wondered why that was until I realized that they're set high so they don't rattle loose and come apart during shipping.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
thanks for the quick response and it makes sense, to make a funny, when the washing machine came to my house I did the new valves and some copper but I didn't take the shipping bolts out of the drum, needless to say when it went to rinse the machine vibrated like a junkie having a seizer, took the shipping bolts out, everything is fine .1
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements