What would cause this?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • hot_rod
    hot_rod Member Posts: 25,045
    A pressure relief valve that is opening and closing could sound like that.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Gordy
    Gordy Member Posts: 9,546
    Should be water traces from the relief valve popping if that is the case. I see the pipes shaking in the background in the video of the water heaters in question.
  • JUGHNE
    JUGHNE Member Posts: 11,410
    AO Smith Cyclone, bad misfiring combustion....maybe water in the burner compartment....poor venting/combustion air set up.
    I have had this happen, wish I had never seen/installed that heater. Over sensitive to anything slightly out of parameter.
    IMO
  • delta T
    delta T Member Posts: 884
    hmmm, I have been asked to install a cyclone (would be my first) for a hotel. It is one of 5, the existing venting is questionable. Maybe I'll pass on this job.....they already bought the water heater anyways, and I have months of work to get caught up on as it is......don't need a callback nightmare.

    Thanks @JUGHNE!
  • Intplm.
    Intplm. Member Posts: 2,633
    Almost sounds like steam flashing against condensate and tripping the relief valve. I wonder what the temperature settings were when this happened?