Does this mean my Grundfos circ pump burned out
Washingtonstate
Member Posts: 1
Hi everyone,
I think I know what this means but thought I'd check with the experts on this site. See attached two photos. The pump itself is too hot to touch, but the line coming in and out are cool. Also, does the burnt label give you a clue that it got toasty? Thanks all.
Doe it still run or has it quit?? Your system could be air bound. The pump if running probably is not moving any water.0
Yeah, that doesn't look good. I'd say it's given all it's got. If it isn't moving water, I'd replace it.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
When the pump impeller stops spinning for whatever reason, the electrical energy cannot be dissipated by movement of the impeller. Instead, it's dissipated as heat and the motor is often too hot to touch.
Luckily, these pumps are impedence protected:
"A method of preventing burning damage when the motor is restricted from rotating; done by setting the motor winding impedance (AC resistance) to a value giving a temperature rise in the windings below the temperature at which burning occurs."8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
it's been hot. Carefully remove the large screw cap, when the system is cooled down, and obaerve if the shaft you see spins when powered, or a screwdriver slot in the shaft can sometimes get them going. They take a lot of abuse, but that may have crossed the line.
There is a specific way to pipe a recirculation pump with thermostatic mix valves, I'm not sure yours is correct?.Bob "hot rod" Rohr
That pump is a little aggressive for what you are trying to move.
You will save some electricity and get more life out of your pipes and circ if you go with something like this.
https://www.supplyhouse.com/Grundfos-98420222-UP10-16-PM-A-B5-LC-1-2-Sweat-Comfort-PM-Auto-Pump"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
If you have a lot of mineralization in your water, the rotor may be stuck. These circulators have low starting torque. Take it apart and check the rotor turning. If it is calcified use CLR and soak the rotor to dissolve the mineralization and give it another go.
I had a pump that wouldn't rotate and when taking it apart a solder ball lodged in the impeller, preventing it from rotating.0