Pump size
I am trying to determine the pump size for a joist bay radiant system
Total btus needed is 22000btu
Total loops 5 equal size
Pex size 1/2”
Longest loop is 250 feet including supply and return
  • Ironman
    Ironman Member Posts: 7,849
    That's 4.4 gpm at a 10* delta T and about 3.5 ft. of head. I'd use a Grundfos ups15-58 on low speed.
    Bob Boan
  • savebtus
    savebtus Member Posts: 6
    Thanks Ironman, can you tell me what fourmula you use to calculate the 3.5 ft of head? I seem to be coming up with much more.
  • Ironman
    Sorry about that, I used 100' instead of 250' which would give you 6.425' of head.
    You can expect about .75 gpm per loop X 5 = 3.75, call it 4 gpm. It still puts you on low speed with a ups15-58.
    The head calc is from the attached chart:
    Bob Boan
    Steve Minnich
  • savebtus
    Thank you, at least I know I’m not going crazy.
    it’s funny, I talked to a few guys at the supply house and each one recommended a different pump, one recommend the same pump you did and one recommended the taco 007 or 008 but looking at the curve charts each one is amazingly different. I think listening to them makes me second guess everything
  • Ironman
    The 15-58 covers both the 007 and 008 depending which speed is used.
    Bob Boan
  • savebtus
    Thanks for the help Ironman!
  • Dave H_2
    Dave H_2 Member Posts: 621
    What about a mixing valve, that can also add some head loss to the mix
    Dave H
    Dave Holdorf
    Taco, Inc
    Ironmandelta T
  • Ironman
    Dave H
    A very valid point.
    Bob Boan
  • delta T
    delta T Member Posts: 884
    OP, You only mention the longest loop length, how close in length are the other loops to that?
    savebtus
  • savebtus
    I made a point to make each loop very close to the same length.
    With all the very different opinions on the head I’m still conserend about the pump what pump to use.
    When I calculate the head accounting for fittings and valves I come up with about 15, that sounds high to me.
    The last thing I want is a to small or oversized pump.
  • Ironman
    Unless you've got a completely crazy piping arrangement, I can assure you that a 15-58 or a 008 will be more than sufficient. I've got jobs with 14 250' loops and one 15-58 on medium speed is pumping them just fine.
    You're over-thinking this.
    Bob Boan
    delta T
  • savebtus
    Over thinking is what I do, I appreciate your assurance, with that, I will use 15-58, the 15-58 based on my original calculations is what I decided, until others at the supply house started adding their opinion.
    Thanks again !