1 pipe steam systems...

with radiators below the water line. I’ve reviewed some jobs via pictures and in this situation. 2 pipe steam radiators are being used with traps. I assume this has to be a pumped wet return setup? I, unfortunately, was not able to see pictures of the boiler room.
Steve Minnich

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,382
    yes. no other way to do it. condensate pump or vacuum pump.

    just wondering why your post says "one pipe steam"??
    Steve Minnich
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    Because the entire building is one pipe except for the apartments in the basement, which are two pipe. I should've been clearer.
    Steve Minnich
  • Danny Scully
    Danny Scully Member Posts: 1,462
    Maybe they’re just filled with condensate @Stephen Minnich
    Steve Minnich
  • jumper
    jumper Member Posts: 2,471

    Maybe they’re just filled with condensate @Stephen Minnich

    Or something along similar lines. Higher floors have ample capacity for gravity return. Special strategy for bottom floor.

    Steve Minnich
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    I’ve been seeing this a lot in 100 year old buildings. In a limited amount of time, I’ve looked into as much as I could but nothing concrete yet. Dead Men aren’t telling any tales.
    Steve Minnich
  • AMservices
    AMservices Member Posts: 611
    If it was meant for gravity hot water the radiator would have a bleeder valve off the top rather than a steam trap or air vent on the side.
    Is there a steam trap?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,382
    @AMservices he mentioned traps in his first post.

    I have seen a couple of these "mixed systems". I always looked for clues weather they were "add on's" or original but they usually seemed to work ok