Hello everyone,
So I live in a 1925 house with one-pipe steam that is operating just fine. I have a Weil-McLain EG/PEG that is in good shape. It has a hot water loop off of it for the basement. If I keep the steam system, I will probably get a heat exchanger added so the basement can be on an independent hot water loop.

I'm about to put the house through a big renovation (floorplan stays the same, but new wiring, floors and bathrooms, mini split air conditioning) and the contractor recommended converting the house to hot water heat.

My steam system is working just fine. My main complaint is the location of some of the radiators, which I want to recess into the wall if possible. But given that everything is going to be opened up anyway, should I make the conversion to hot water? The heat would still be distributed via new radiators (my pocketbook is not ready to jump to radiant flooring yet).

Would the increased efficiency due to the boiler and room-by-room zoning make it worth it in the long run? I hope to be in this house for the next 50+ years, and we will definitely be here for at least 10.

Thanks in advance,
Jackie

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    In one word. No.

    Don't do it. If -- and it's a big if -- you could reuse the old radiators, and if -- an even bigger if -- you could reuse some of the feed piping, all the radiators would have to be converted to hot water (old vent removed, new air bleeds installed, return opening plug taken out, probably new valves). Then new piping -- it's unlikely that you could use all the feed piping, and you'd have to run new return piping anyway. Then of course a new boiler and pumps and controls. If you went for new radiators... they aren't cheap.

    And for why? You might make a slight gain on efficiency, but I doubt very much that it would be anything near to recovering the investment. You won't make any gain on comfort; if you don't need to change the temperature on a room by room basis daily you can adjust the room to room balance with the vents. If you do, you can get thermostatically controlled vents.

    Moving a few radiators is no big deal -- but if your contractor is recommending changing from steam to hot water, he doesn't know what he's doing with either one. Find someone who knows steam to make the change.

    So again, bottom line -- don't do it. Waste of big bucks for no gain.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjdCanucker1Matthias
  • HVACNUT
    HVACNUT Member Posts: 5,835
    Options
    @foresthillsjd

    You sir, know not what you have done. You have soiled the sanctity of this sight. Prepare to be bombarded. And your contractor will be hunted down like Frankensteins monster. They will draw him in with the soft sounds of a purring circulator.
    You dont want to know what happens after that.
    DROP HEADER!!
    foresthillsjd1MatthiasSeanBeans
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,967
    Options
    Agree with @Jamie Hall.Also, no reason to use heat exchanger for basement unless you have water loop piping that's above the boiler water line. No brainer.
    foresthillsjd
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    Thanks for all the helpful advice. This is good to know that it's not even a close decision! @STEAM DOCTOR , I was told that the heat exchanger would be a good safety feature in case the hot water loop in the basement sprung a leap and started draining the boiler. Should that be a concern?
  • leonz
    leonz Member Posts: 1,127
    Options
    If you do not have a low water cut off to protect the boiler you need one!!!!! The low water cut off should be wired as the first control to enable it to shut down the boiler in the event of a water loss to prevent an explosion from the shock of cold water reaching the boilers steam chest.

    You can hang steam radiators on the wall if you want heat the space in the basement and I am sure you can buy radiator covers and paint them a nice color.

    foresthillsjd
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,967
    Options
    Would not be concerned about that. Leaks in the loop are pretty uncommon and you do have a low water cutoff. Even with a heat exchanger there is a risk of leaks in the piping from the boiler to the heat exchanger. I would think that the heat exchanger is overkill.
    foresthillsjd
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    @leonz , don't worry, I definitely have a low water cut off! I'm just the type of person who likes a belt, suspenders, and also safety pins to clip my pants to my shirt.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,967
    Options
    You can install second low water cutoff
  • gerry gill
    gerry gill Member Posts: 3,078
    Options
    I personally think you should keep the steam and i do use heat exchanger's for the water loops. I feel it is a cleaner, more professional job than what we around here call a 'dirty loop'. Its kind of a Cadillac or Chevy thing.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Steamhead
    Steamhead Member Posts: 16,835
    Options
    @foresthillsjd , where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 7,834
    Options
    As long as the LWCO is operating properly you should have no worries. You should flush your LWCO at least once a week to be sure that there us nothing building up in the float chamber. If you are using only a probe-type electronic LWCO then make sure to test the unit monthly by allowing the water to drop below the probe to make sure the burner shuts off.

    You can get a hot water coil for the EG/PEG boiler if the left end section has a proper opening. Use that as your heat exchanger if you want to add that layer of safety. You can add a limit control to stop the burner at 180°F for that zone only. This way if only the basement zone calls for heat you won't be making steam
    Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics