Normal amount of make-up water for residential steam.
Back to this one we installed 3 years ago for a good flushing. The feeder was reset a year ago almost to the day. Used 21 gallons in one year.
Radiator vents are good. No leaks on the returns. Can see one main vent thats kinda buried. That one seems clogged shut. The other main is all boxed in but no signs of leaking steam.
Peerless ECT3 with 8 or 9 rads.
Thanks in advance !
Just figured out how to upload a pic0
that's about 2 gallons/ month, more than that because you don't steam in the summer. sounds high to me0
It depends on the boiler size and operating pressure. At only a few ounces, properly maintained valve packings and air vents will hold all the steam inside, and no makeup water will be needed. If a float type LWCO is installed, then the weekly blow downs will lose some water, but not 21 gallons. Plugged air vents will not use water, unless someone raises the pressure to compensate, but they will use more fuel, and cause discomfort!
Also seems high to me.—NBC0 -
From what I've found it depends on the size of the system. Normal water is lost mainly in the form of moisture every time the system breaths out.
My own system with probe type LWCO (392sqft EDR) peaks at around 16 ounces per week during extreme cold. Probably around 2 gallons per year overall.
I've had packing nuts as well as spud nuts leak only briefly as the system warmed up, so no one would ever actually notice it.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Cedric uses about a gallon a week in the major heating season. None when the heat is off.Br. Jamie, osb
Check to make sure none of the radiator vents are leaking steam. It is amazing how much water loss can occur for one or two radiator vents that don't completely close during a heating cycle and it may not be obvious to the naked eye.
The water level in the sight glass looks a bit high too.0 -
The main vent I thought was clogged actually was leaking steam like crazy. His wet returns are clogged too. I convinced him to have them replaced with the main vents. Semi finished basement so thatll be a chore .......
Thanks for the input !0 -
Hydrolevel makes a great auto feed that tells you exactly how much water went into the system.
Net IBR Rating ------------ Gal/month
BTU/HR Limit
Up to 90,000 ------------ 6
91,000 - 120,000 ---------- 8
121,000 - 150,000 ------------- 10
151,000 - 185,000 ------------- 12
185,000 & Higher ---------- 15
Note: The above limits are based on normal boiler operation during the heating season. They do not include water added as a result of boiler and/or low water cut-off maintenance.1 -
> BTU/HR Limit
Those quantities seem insane. 10 gallons per month for 121-150k?
@Steamhead what are your thoughts?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I would suggest if one goes by those numbers, one will be replacing their steam boiler a lot.GBart said:Hydrolevel makes a great auto feed that tells you exactly how much water went into the system.
BTU/HR Limit
When my boiler got a hole in it I didn't use that much water....think about that.0 -
This is from Burnham's IN series manual.
I think that for sales purposes, hydrolevel needs to put in such numbers. Let's say hydrolevel were to tell you that you should only be adding one gallon per season. Every single buyer will be asking themselves what's the purpose of an automatic feeder if it's only adding 1 gallon per season. Even the most hands off homeowner would be willing to add 1 gallon per season.0
> BTU/HR Limit
That's gotta be gallons per year , right ? Gotta be a typo.0 -
@Ron Jr. said: That's gotta be gallons per year , right ? Gotta be a typo.
It seems high even for a year. I have a 35 year old Burnham, Net IBR Rating of 207,800 BTU/HR and I use about a quart a week for blow downs (they even exclude the blow-downs from their numbers), during the winter months and I may use another half gallon during the coldest month of the winter season.
You really need to make sure all vents are properly closing and all couplings, at the radiators aren't leaking. Many times the leak is so subtle that it just steams away and isn't obvious to the naked eye.
This.Fred said:@Ron Jr. said: That's gotta be gallons per year , right ? Gotta be a typo.
And, @Ron Jr. - good to hear from you! Still doing those boiler-in-a-bottle installs?
Consulting0
- 167 Indoor-Air Quality