Oil Primary Control Reliability issue
Thanks in advance.
Darin
Those units have a goodly complement of electronic whizbangs in them. Which leads me to the first thought that comes to mind: how clean is your power supply? Doesn't take all that much in terms of spikes, voltage dropouts, or just plain crummy power to make them lose their minds... with that many failures in close succession, that would be the first thing that hit me.
Don't rely on your power supplier's pious statements to the effect that their power is perfect. It isn't, even when it leaves the generator -- and by the time it gets to your site it may be pretty bad. Power conditioner or UPS?Br. Jamie, osb
Another thought...check your neutral and building ground.. are you getting any stray voltage..0
Properly installed components usually last quite a long time. Many older burners/furnaces/boilers aren't properly grounded. Newer electronic controls require proper grounding.
Another problem may be improper venting, dirty heat exchanger and/or poor draft causing heat build up during the run cycle, and/or after shut down.
Electronic components don't like excess heat either.There was an error rendering this rich post.
Agh yes. Hadn't thought of a bad neutral (and not necessarily on the burner circuit -- anywhere on the building side of the transformer will do it). That can give some huge voltage spikes or drops. And a bad ground (never mind a missing one) is simply lethal to digital electronics.lchmb said:Another thought...check your neutral and building ground.. are you getting any stray voltage..
Morning all. This goes back to my "hardier" comment. The house is in a rural location near the end of the line as far as power goes. Voltage spikes, lightning strikes and outages (Oh My!!) are common. Sometimes we need to fire up the generator to make it through a bad snow or rain storm. Knowing that dirty voltage can play havoc on some controls that I believe are over-engineered and have functions I'll never use is kind of a waste to me as well as inconvenient if the module goes bad. Other things aside I think I need to relocate the control or put a shield over top because I know there isn't a chimney cap on top and think rain water may be coming down it and dripping onto the board. Still curious about a reliable replacement without all the bells. Thanks
Darin0 -
BTW Cabinet is grounded to the panel. House was built in 1970 and has a Cutler-Hammer panel using 12 gg solid wire0
I quite agree with you about fancy controls which are fragile. Seems to be the coming thing.
Do put some sort of moisture shield over the control or relocate it -- it doesn't take much moisture to ruin these things. For power, though, I would look into a UPS such as one might use to run a computer through. They aren't really all that expensive, and they solve a whole lot of problems with dubious power.Br. Jamie, osb
What, if anything, is hooked to the Envirocom terminals on the control?DWallis said:The error I'm getting on this last one is a "Enviracom Communications Error".
Consulting0 -
Here is the manual, showing the various error codes:
https://customer.honeywell.com/resources/techlit/TechLitDocuments/69-0000s/69-2467EFS.pdf
An EnviroCom error can also be a low voltage error. You might want to get hold of a recording voltmeter to see what's going on with the incoming power, and get after the power company if the problem is on their end.
Low voltage can cause delayed ignition, which can make the burner "puff" on start-up. This is NOT a good thing.All Steamed Up, Inc.
Consulting0 -
These aren't "fragile" controls. They have been in the field for many years, well over a million in total. Something is wrong with the installation or site conditionsTo learn more about this professional, click here to visit their ad in Find A Contractor.1
In defense of my comment. Fragile is a relative term. In relation to some things, your are quite right, @Robert O'Brien -- they've been used for a long time quite successfully. As you note, they are, however, sensitive to site conditions or installation problems in a way that a simple SPDT switch (think pressuretrol or bimetal Aquastat -- never mind a Honeywell T87) isn't. Specifically, "dirty" power can cause problems. A bad neutral somewhere in the local system can cause problems. A bad ground. That's all I meant.Br. Jamie, osb
"Other things aside I think I need to relocate the control or put a shield over top because I know there isn't a chimney cap on top and think rain water may be coming down it and dripping onto the board."
woah, these controls, any of them, CANNOT GET WET OR DAMP, that is why they are failing, and no "hardier" control is going to fix this
you are running the risk of serious injury, home damage, or death, any oil or gas safety control that has gotten wet MUST be replaced
the controls are defaulted to test memory at start up and if they don't pass muster they lock themselves out0 -
please see my comment aboveRobert O'Brien said:These aren't "fragile" controls. They have been in the field for many years, well over a million in total. Something is wrong with the installation or site conditions
Lighting stikes are a likely canidate. Had ones that blew out our TV, but may have been caused by voltage difference between comcast TV and power cables.
Had a ~ 1 amp continuously on roof ice melting cable, fused it at 3 amps. Found fuse had blown couple times months apart, no lighting here in winter.Everything looked good, can only assume it was a voltage surge. Was powered off a HVAC power line, but in winter AC pump (the MAIN HVAC load) didn't run, only blower motor for gas hot air. Was a restaurant on a MAIN city street. 120/208 3 phase 400 amp service, HUGE pole transformer only <200 ft away
If you think have voltage spikes maybe put a whole house surge suppressor at the breaker panel. supposedly they have a higher Joule rating than those computer power strip ones. Only thing is I think all of them clip at ~ 330V , not sure on that number. Sine wave peak of 120VAC is 170V
To be specific , Technically not ground but a bad or lost neutral can cause huge voltage swings ( utility line from street doesn't have a ground wire only the neutral wire (at ground potential). We had a bad one once, some lights were dim others super bright, utility used a outdoor crimp connector on neutral that they latter found liked to corrode.0 -
doubt it, read my comment above, his controls have been getting wet, game overLeonard said:Lighting stikes are a likely canidate. Had ones that blew out our TV, but may have been caused by voltage difference between comcast TV and power cables.
To be specific , Technically not ground but a bad or lost neutral can cause huge voltage swings ( utility line from street doesn't have a ground wire only the neutral wire (at ground potential). We had a bad one once, some lights were dim others super bright, utility used a outdoor crimp connector on neutral that they latter found liked to corrode. </p>0 -
I don't know they've been getting wet, I suspect they may have been getting wet. I'm just asking if others have noticed issues in rural areas with the primary control. If the controls have been proven reliable in normal conditions, I will look for other suspects which include but not limited to possible water dripping from the vent. I haven't seen it, I suspect it(highly). Thanks for all the help.1
Technically our controls are solid as a rock, all the bad ones were weeded out long ago.
Also look into a whole house surge suppressor.