Cold Sandwich Eliminator with Circulation Pump- Is this diagram correct?
dhurst12
Member Posts: 6
Installing a mod con combi and want a cold sandwich eliminator, and hot water circulation pump. Problem is, that the electrical panel has no space for a breaker for an electric WH and existing circuits are inadequate. Therefore, plan to use the aquastat on the WH to circulate thru the boiler to maintain the temperature. I think the attached diagram is correct (note that isolation valves are not shown), but want to get some feedback. Also, I want some opinions on the thermostatic mixing valve. It is required or just nice to have? Will it work as shown on the diagram?
I don't see how flow will be induced in the mixed/hot line going to the fixtures unless the recirc pump is running.Bob Boan
Thanks Bob,
But I'm not sure I understand your concern. The normal flow, if the circulator happened to be off, would follow the dotted lines shown below:
I think I see a problem with my proposed system. If the aquastat is set at say 130F and the mixing valve is set at say 120F, will the mixing valve totally shut off the hot water flow when the system is trying to recirculate since cold water can't enter the loop.
Do I need the mixing valve at all?0 -
A new ASSE standard in the works that proposes instantaneous WHs can regulate their output as accurately as a thermostatic mix valve and should be able to meet that + or- temperature requirement.
Also a thermostatic valve needs the hot supply to be about 25° warmer than the mixed output temperature to perform accurate temperature regulation.
Looks a bit like a tank style water heater you are buildingBob "hot rod" Rohr
cmon Hot Rod, tell us more...
Tom
Montpelier Vt0 -
Here is a good explanation of the ASSE 1082, 1084, & 1085 standard in development.Tom said:cmon Hot Rod, tell us more...
https://www.workingpressuremag.com/water-heaters-used-for-temperature-control/Bob "hot rod" Rohr
If you use a recirculating pump with a thermostatic mixing valve you wil need a thermostatic control to shut off the pump before the returning water reaches the mixing valve’s setpoint or it will cause problems with the valve due to it having the same temperature on the cold side (recirc return) and a hotter temp on the hot side. I use a Honeywell strap on aqua stat so I can adjust the shutoff temp, or a pump with a built in thermostat0
A couple things can happen if a record is not properly piped to a thermostatic mix valve. The loop temperature can droop, due to lack of hw being added to the loop, or the loop temperature can drift up to the tank temperature if the valve cannot see a H&C cold differential to mix properly.
The correct piping has a balance or globe valve to adjust the correct amount of recirc flow to offset the heat loss around the loop.
A sensor at the return to the recirculation is a good idea, it may not guarantee the most distant fixture has adequate temperature on a long loop, like a large hotel for example. Better to run the pump and modulate flow, or pulse it to assure the entire loop is being maintained.
I doubt you would ever see the return the same as the supply? Possibly a very short, well insulated loop? But then you may not need recirc? if there is little heat loss from the HW piping.
I think the newest plumbing or energy codes require recirc on any distance of over 50 feet from HW source to distant fixture.
Idronics 11 and 21 cover the topic of DHW recirculation.
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 994 Plumbing
- 391 Solar