vaporstat wired in series with pressuretrol
Options
josephc
Member Posts: 39
Does anyone have a diagram showing how to wire these two instruments in series? Also my pressuretrol doesnt have an R or B label on either terminal.
What i have done is wire #1 from boiler to term R on vaporstat and then connected a wire from there to the pressuretrol on one of its terminals. Then the other wire #2 from boiler to the B terminal on vaporstat. Then a wire from there to the other terminal on the pressuretrol. Is this considered in series since going through both switches?
Thank you
Joe
What i have done is wire #1 from boiler to term R on vaporstat and then connected a wire from there to the pressuretrol on one of its terminals. Then the other wire #2 from boiler to the B terminal on vaporstat. Then a wire from there to the other terminal on the pressuretrol. Is this considered in series since going through both switches?
Thank you
Joe
0
Comments
-
No. You've wired them in parallel. Boiler, terminal R on vapourstat. Terminal B on vapourstat to one of the pressuretrols. Other terminal on pressuretrol back to #2 on boiler -- assuming you have no other safeties. If there are other safeties, then go to them before you go back to the boiler.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -
Thank you; Ive corrected it. Since there isnt an R or B on the pressuretrol terminals is it correct to assume it doesnt mater which one is wired to the vaporstat and which continues on to the boiler.0
-
Correct. It's just a simple switch.josephc said:Thank you; Ive corrected it. Since there isnt an R or B on the pressuretrol terminals is it correct to assume it doesnt mater which one is wired to the vaporstat and which continues on to the boiler.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Jamie Hall is correct assuming the pressure control is a "break on rise" pressure control with only two terminals which is the most likely senario-1
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements