Water heater demand
Nycwrenchturn
Member Posts: 19
I have a customer who runs a brewery . He has always had hot water issues . He needs 170 degree water for 1 hr constant using 3 hoses to clean the tanks . The hoses have heads on them that put out 10-15 gpm . Needless to say he runs out of hot water pretty fast with what he’s got now . Can anyone help me . I was thinking of putting in lochinvar armor condensing heater with storage tank or tanks . Or Ao smith gwh -1000 boiler with storage tank .
Come one guys . Need little help here0
15 GPM times 60 minutes equals 900 GPH. 900 gallons times 8.34 lbs per gallon equals 7506 lbs. 7506 times 125 degree rise equals 938,250 BTU/hr.0
Ok . But each head does 10-15 gpm so it’s triple that0
Not sure if there is a feasible system for this guy0
Or i was thinking of splitting the hoses to two different systems . And not having all three work off of one heater0
Question why he needs nossels with 10-15 gpm, that's a lot of flow.
Maybe suggest better nossel. Higher speed jets to clean better with less flow. Had similar solution for distilled water rinse station at work once.0 -
a few choices
lower the load
split the load
storage for the dump load
a bank of tankless
seem more and more breweries are going to low pressure steam boilersBob "hot rod" Rohr
That’s a great point Leonard0
Would steam do the job and not require the huge volume he uses now?0
He has a low pressure steam boiler in the now with 119 gallon storage tank and heat exchanger0
Lower flow seems to be a pretty quick partial solution. Given the 45 gpm total flow, 14 tankless would cover it with built-in redundancy if one fails for any reason.
Tankless capacity: BTU/h input / 500 / delta-T = gpm per tankless.
(Times EF rating for true gpm output)
199,900 BTU/h / 500 <8.33 x 60 minutes rounded> / 125 degree rise = 3.2 gpm/tankless. 45 gpm / 3.1 gpm x .97 = 15 tankless and will never run out and will not need to heat storage while not in use.
Reduce the flow and reduce the number of tankless needed.There was an error rendering this rich post.
Do you know why they need 45 GPM of fresh water for cleaning? There are different ways to clean the tanks that could use less water, depending on set up. Do the tanks need elevated temp for disinfection? Can the tanks be heated or are they just receiving vessels? Are those heads on different ports of the same vessel during the cleaning?You can have it good, fast or cheap. Pick two0
Just an update . I installed a lochinvar 501 and it kicks butt . Highly recommend it0
Just go tankless. Set of 8 cascaded should do it. Make sure brand you choose has good commercial warranty. Off the top of my head each should run 2 gpms at that temp rise. That’s 16 gpms on coldest day. Build a cascade system with common venting and common headers. Done deal. 1.6 mill btus is normal
Please do thorough research at how many gpms at 120 degree rise. I think I’d go with this setup. Plus you get solid redundancy. If one or two units go out, he won’t stay out of business as opposed to having big single unit. Plus he should get maximum efficiency.0 -
Years ago I had a process hot water system that need twice a day high/hot flows. For that particular system I wanted to get to the highest flow from each of the tankless in a rack. As the tankless are flow restricted at high temp rise I was going to need a lot of them. Instead I put two 120 gallon tanks ahead of the rack of tankless. I think it was 6, 199,000btu Rinnai. Given that the water was needed on a schedule, twice a day I had the bank of tankless preheat the two tanks to 120 just before the call. Once up to temp when the call came I was getting 8gpm output per tankless at the required high temp. Wish I could detail that better but it was 16 yrs ago1