Primary/Secondary Piping
KeenGreen
KeenGreen Member Posts: 27
In recent months i have been given 2 different ways to size my primary loop using a Mod/Con boiler.
some say to use the output of the boiler to size the primary while others say to size it to the heating load required. Anyone know which way is best practice?
Thanks
KeenGreen
Learning as much as I can to be better than I am.
    HVACNUT Member Posts: 7,446
    As long as the piping is sized to handle the load of the primary pump. The manufacturer should have everything spec'd for the near boiler piping.
    The secondary manifolds can be generously sized.
    kcopp
  • Steve Minnich
    Steve Minnich Member Posts: 2,876
    The net of the boiler should be the same as the load (heat loss).
    Steve Minnich
  • Ironman
    Ironman Member Posts: 7,903
    It depends what you mean by "primary loop". Most of the time, pro's refer to the loop to which the expansion tank is connected as the primary. Most diagrams and manuals ID it that way too. Is that your meaning or are you referring to the boiler loop?
    In either case, ANY loop has to be sized based upon the flow rate (gpm) that's required in it. That's based on how many btus are required at the delta T required. The universal hydronics formula: Btus = (gpm X 500) X delta T. Any of the components of the formula can be moved to find the values of the others. 500 is a constant that stays within the parenthesis.
    Thus, at a standard delta T of 20*, an 80k btu boiler would need a flow rate of 8 gpm. That would require a 1" pipe.
    Look at the diagram below. I would generally consider what is flowing straight through the run of the tees as primary and what's going through the bull (side) of the tees as secondary. The boiler could be in either loop and therefore could be in either the primary or secondary.
    Bob Boan
    KeenGreen
    EBEBRATT-Ed Member Posts: 20,177
    Either way size the boiler loop for the maximum boiler output at the TD of the water 20, 30 or 40 degrees. Size the heating loop for the heat loss or better yet the heat emitter output
  • Rich_49
    Rich_49 Member Posts: 2,783
    500 is only constant in systems using 100% water as the fluid . That number can change when Glycol is used and at different concentrations . gallon of water 8.33 pounds
    Hour x 60 minutes
    499.8 pounds (500)
    732-751-1560
    Rich McGrath 732-581-3833
    KeenGreen
  • Steve Minnich
    edited May 2018
    When I talk to customers, the words primary and secondary rarely get used. I just use boiler loop and system loop, makes it easier for them to wrap their head around. But yeah, primary loop is usually the system side.
    Steve Minnich
    Rich_49KeenGreen