Problems with shared return on new oil heating installation
melro
Member Posts: 2
in Oil Heating
I'm really hoping someone can offer some advice. I recently had installed a new oil heating system. Its a large installation with 3 zones and water. All the zones have a shared return due to lack of space for individual returns for each zone, therefore a shared return for all zones has been installed. It now seems that when an individual zone is on that the water returning from the heated zone migrates through the return to the other zones which are off, causing the radiators in the zones that are switched off to heat up. My question is how can this be resolved?
Flow check on return0
before they join together to create the shared return. Slightly less effective, but will also work, is a flow check on the feed.Robert O'Brien said:Flow check on return
This.Robert O'Brien said:Flow check on return
Consulting0 -
@Big Ed is right. If you split one zone the returns need to connect back together before entering the common return. Otherwise you will need check valves. But eventually check valves will fail.
Two pictures attached from B&G system design manual.Never stop learning.0 -
Thanks very much for all your helpful replies. I would be interested to know why you think the check values will eventually fail?0
sad experience..Br. Jamie, osb
Because time is cruel and eventually everything fails. I’m sure they’d last a good long while though.Never stop learning.0 -
Adding a more complicated device to correct a simple solution just increases the odds of failure ....
- 120 Geothermal