Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Replacement air vents for near boiler piping

aarondavid
Member Posts: 9
Hello all. Enjoying this powerful resource. After reading Dans book i realize my heating systems need attention. I have severe water hammer and a cold radiator on the second floor. These are the currents vents installed and would like to start there. Looking for suitable replacements. Thanks in advance!!




0
Comments
-
-
0 -
Better pictures would help a lot but it looks like your returns are tied together above the boiler water line. That will cause water hammer.
Main venting needs to be sized based on the diameter and length of the mains and the amount of air you need to expel. Gorton #1's are small, unless your mains are short. You really can't over vent a main. I like the Barnes and Jones Big Mouth, available from Amazon. Gorton #2's are good also but the Big Mouth has twice the venting capacity of the Gorton #2 at the same price.-1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 945 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements