Pressuretrol settings

Mike_Sheppard
Member Posts: 696
What do you guys normally set this specific Pressuretrol at? Am I right I’m assuming this is not the best Pressuretrol to be used for low pressure steam heating?
Would you set this at 0.5 cut in with a differential of 1?
I’ve been seeing these a lot lately instead of vaporstats. The last one I came across had the (very small) building running at 9 PSI....
And a picture of the master trap that’s here just for some facepalms...
Would you set this at 0.5 cut in with a differential of 1?
I’ve been seeing these a lot lately instead of vaporstats. The last one I came across had the (very small) building running at 9 PSI....
And a picture of the master trap that’s here just for some facepalms...
Never stop learning.
0
Comments
-
Going to need more pictures and information. 9 psi is pretty high. Is that an equalizer with a open atmosphere drain or is that an overflow for pump?0
-
that honeywell pressuretrol is a stand for low pressure steam turn it down to .5 and the system will work much better, unless there are other problems??"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
.5 and a Differential of "1" is the best you can do with that Pressuretrol. Below that, you'll want a vaporstat.0
-
@the_donut - the master trap picture was just for fun. 9psi was another building not this one. I was just wondering if there was a reason I keep seeing people install this pressuretrol instead of a vapor stat.
@newagedawn - it's currently operating that way already. Was just wondering why people are using this control over a vapor stat.
@Fred - thanks. Not sure why people in this area keep using these over a vaporstat. It's rare that I even see a vaporstat anymore...Never stop learning.0 -
@Mike_Sheppard , That Honeywell 404A is the standard Pressuretrol used on most 1 and 2 pipe systems. Vaporstats are great but cost a little more and are typically only required on Vapor systems that must operate at or below 12 ounces of pressure.
I have a one pipe system and I happen to have both controls on my boiler. The Vaporstat is the primary control and the Pressuretol is a back-up, should the Vaporstat fail.1 -
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 945 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements