Prestige Triangle Tube Solo 110 Failed Ignition error code E1 and violent vibration/noise
bushman432
bushman432 Member Posts: 17
My boiler is almost 5 years old with no issues, but has had a few "Failed Ignition" errors in the last few days . I did some searching on this site and found other information mentioned around a possible bad ignitors. This boiler is on it's original ignitor and has 36,000 ignitions between DHW and CH. I just ordered 2 as I assume this wall will advise me to replace it (the installer didn't mention this for preventative maintenance) and then I'll have a spare. I also completely cleaned the condensate drain as it was pretty full of residue.
Everything ran normal for another 46 hours with no errors when I heard a loud racket in the garage, investigated and the boiler was vibrating violently and making a lot of noise. I didn't video that incident but did record a minor one which is more of a pulsing sound with less violence, but file attach and image attach didn't allow me to attach it here. Does anyone know what that noise is, is this all related to ignition or something else? I appreciate any help, and am also curious what damage could be done by these combustion issues or whatever they are. Also if anyone knows how to attach an Android VID file here let me know so you can hear it.
  • DZoro
    DZoro Member Posts: 1,048
    Sounds like the venter fins may have broken up. Take the grey elbow off and look into the venturi towards the venter. You may or may be able to see the issue. Best then would be to remove the venter and inspect it, and the combustion chamber.
  • bushman432
    The installer inspected the elbow and it was only slightly roughed up and he said the fins were fine...he did pull the ignitor and clean it with scotch brite and reinstalled and said he would pull the combustion chamber apart and inspect if I wanted but he didn't think we need to (and didn't). The unit ran fine for another day. Noise happened yesterday and I tapped the Grundfos internal pump and the noise stopped but I don't really know if that was the source. The pump is quiet, if bearings were going bad wouldn't I hear it all the time?
  • DZoro
    Hmmm, can you take the grey elbow off and take a picture of the venture (part on the gas/blower) where the elbow connects. Also a picture of the vent pipes outside. Still suspicious, I think your right may or may not be the pump. When you tapped on the pump you also had the door off. Which changes your intake air......
  • bushman432
    Pictures attached, let me know if others needed. Of note when this first happened I did find the exhaust screen was cocked in the PVC roof penetration at the top (on roof) but no signs of critters in any vents but I can't see in that sealed 90 in the attic.
  • DZoro
    Was the screen turned like something could have gotten in? If so I would cut open the exhaust pipe in between those 2 90*'s. Then take the pipe off on top of the boiler and confirm nothing made it all the way down to the bottom. I believe on that model you can also peek up from where the condensate drain trap is, just unscrew the trap and remove. You should be able to look up and see the piping.
  • bushman432
    Yes there was room for something small to get in. If something were in there why would the boiler run fine 99% of the time? I did find some debris in the condensate drain trap when this all started and no idea when or where that came from, see pic. My wife took a good video of the cyclical noise, once it downloads I will post it here. Thanks for helping with this Dennis. I'd like the wall to see the video before I cut the exhaust open...
  • DZoro
    Any blockage/resistance in either the air intake or exhaust greatly affects it's operation and will cause some of the issues you are having. I just got back on a same type of a issue today, found a nest of helicopters/sticks......I don't know what that is that you found in yours, eggs? Is there enough room to lift the exhaust pipe off on the top of the boiler without cutting?
  • bushman432
    Here is the video, the vibration and noise escalates until the unit was turned off at the very end.
    https://youtube.com/watch?v=MWoxwEXjJZc
  • DZoro
    You may have two issues here. First ignition, and your tech fixed. Second noise, which may or may not be combustion related. It maybe pump/water related also. That unit has a three speed pump it is currently set on high, try the medium speed (2)
  • DZoro
    After listening to that I'm thinking combustion. Something in the piping or back to your combustion blower......
  • bushman432
    The next time the event is happening or now? It has been on high since the install 4.5 years ago.
    SuperTech
  • DZoro
    You can leave it on high. Don't think the pump is your issue.
  • DZoro
    Is that black piece that you found plastic????
  • NY_Rob
    NY_Rob Member Posts: 1,370
    Can you get your tech back with his combustion analyzer?
    Maybe running lean, almost fog-horning...
    If it hasn't had it's mixture checked in 4+ yrs it's due.
  • bushman432
    Perfect timing, I've had the unit off to take those pictures, fired it up and the noise started from cold start. I switched the pump to Med and nothing changed, switched back to Hi. I touched the gray elbow to the venture and it stopped but I didn't really feel anything. I'll try to locate the source better next time.
  • DZoro
    When it starts making the noise again, take your hand and slowly cover the gray elbow until the sound stops. The venturi appears worn in the 2nd picture. Unusual due to the way it is piped but is possible.
    SuperTech
  • Zman
    Zman Member Posts: 7,611
    I would inspect everything including the fan.
    Combustion analysis should be on the list.
    Sometimes you can get a noise like that that is caused by harmonics in the gas line. How close is the boiler to the house regulator( at the meter). Does the regulator hum like that?
    Albert Einstein
  • DZoro
    Fully agree combustion analysis needs to be done. But it looks like there maybe some repairs needed, possibly fan, venturi, or exhaust cleanout. Any of these can cause the noise issue. Gas is also a possibility but the noise actually sounds like a rattle. Like bad/broken fan fins. If a slight restriction on the venturi works then a venturi replacement will be necessary.
  • bushman432
    Answering questions:
    1. On top of the unit the air vent cap is loose as it should be and the emergency pressure relief works (checked these first).
    2. the venter fan spins freely and smoothly but feels loose, it will wiggle or flex away when pressed carefully with a screw driver.
    3. Foghorning: unit has done this from the beginning of time but has gotten louder. I didn't know what it was called but it sounds like a horn to me and have mentioned it since the install.
    4. Debris in condensate drain trap: 2 pieces of Styrofoam, and black is soft flexible rubber. Tech thinks the foam may be from original packaging as he found a small piece in the cabinet. The intake is completely clear. The exhaust looks like a healthy smoke stack in the cold of the morning. I just shined a flashlight down the exhaust and I see standing water at that first 90 from the top.That looks bad. Assume I should cut that 90, drain it and reinstall at an angle down instead of a flat square double 90???
    5. My tech told me Thursday he doesn't have a combustion analyzer. He is the most experienced with TT in town I believe...
    6. The gas supply meter is 60-80 feet from the unit and is quiet right now. I could check again next time this happens which may be soon as I'll do another cold start up.
  • lchmb
    lchmb Member Posts: 2,997
    If this unit has never been set up properly (foghorning from beginning tells me this) than you need someone in their with the proper equipment to start. I would recommend finding someone with an analyzer, have them contact tech support while on site and have them walk through the initial setup. Foghorn sound is caused by the readings being out of balance.. it will never get better without proper adjustments.. I would also keep a very close eye on the pvc venting. Discoloration is an indicator it has been running to hot. You may wish to look into having it replaced..
  • DZoro
    Yes you are correct should not be any water in that pipe. Chances at good that something is holding the water in the pipe.
    Your tech needs a combustion analyzer he cannot perform your job properly without one. That unit should never make any noise when set up properly.....
    lchmb
  • bushman432
    Thank you to everyone for the ongoing tech support - as you can tell I need it due to the newbie factor!
    A few more details, I am at elevation as Flagstaff is at 6800 feet.
    I will ask my tech to read this information you all have posted, and I will make some calls Monday to figure out if someone local or close has a combustion analyzer that can be used while talking to TT tech support.
    Here is an image of the small PVC elbow venter intake with discoloration.
  • bushman432
    Forgot a few other details, the 2 90s in the exhaust PVC are in an attic at ambient temp so it gets freezing temps every night here. I drained a few gallons from the condensate drain trap over the last hour but will replace the 2 90s with 45s or something to create a slope to the drain trap soon.
  • bushman432
    Harmonics started again (thanks Zman) and per Dennis I slowly restricted intake flow with my hand and yes the harmonics stopped. A few moments later I removed my hand and the unit continued to run smoothly. So this means the venturi needs replaced per Dennis statement above?
    With less air at time of ignition the unit works better so Zman called it and it may be running lean on the gas/air mixture here at 6800 feet elevation.
    I will also spend some quality time educating myself with the Caleffi training videos...
    Happy Super Bowl Sunday everyone, I hope we all get a good game, and as a Broncos fan I hope the Eagles pull off a stunner!
  • DZoro
    new venturi, slope pipe, have combustion analysis done per mfr specs. You should be good to go, and now for the commercials.......:)
  • bushman432
    Update 2/7: - got the exhaust replaced with 45s and a nice slope Tuesday.
    - tech used brush in bottom of unit from condensate drain and cleaned a few large bugs out but no nest or significant debris in there (as much as you can tell without being able to see anything) or the exhaust flue. Assuming the original 90s were just too flat and water accumulated.
    - unit worked good at start up after that, tech verified some parameters with settings from TT, CO in exhaust stack I believe and checked something in the gas valve that was acceptable.
    - he also checked gas line pressure was in acceptable range at the unit and it was
    - sound started slightly again last night a few times
    - shut unit down to go to work
    - at lunch today, turned unit on and got a slower pulsing of the original but similar, see video below. As typical, this happens at cold start during ignition cycle. This time reducing flow with my hand didn't affect it, event lasted a few minutes and then went away. Way less violent than original video at top of this post.
    - Dennis: do you still believe this has something to do with the venturi, and if so what is happening with the venturi to cause this?
    - any other ideas out there? Can't see the venter fan very well through the venturi hole so could disassemble to fully inspect?
    - good thing we are having a warm spell or I would be in a world of hurt here as I'm only running it when I am home in case something goes catastrophic...
    https://youtu.be/UnuVLrwcHXQ
  • bushman432
    Also, when checking the information menu I do have a few "sensor drift" errors the manual describes as "supply or return sensor reading has drifted." But I have seen that when I start it back up after turning it off manually a few times on the display.
    Just to be clear, after this video pulsing stops shortly after start up the boiler runs great completing DHW cycles and the CH cycles for hours. Typically the cold start up when its been off for extended periods during the night etc is when this happens.
  • DZoro
    It's hard to see in the pictures but it looks like there is deterioration on the right side of it. Would be unusual because usually re ingestion of exhaust gasses cause the deterioration. In your case that is not probable. Inspection of the blower and burner chamber should still be done. How long is your intake pipe, and does it still do it with the door on?
  • DZoro
    Sensor drift can be caused by improper piping or flow of water.
  • bushman432
    Still does it with the door on, I just took it off for the hand remedy and videos. I put the door back on after this new tech work but took it off when it happened again. The intake pipe is 26" from cabinet up to the open attic. The attic has a plywood floor, lots of open vent space and at outside temp. We can do the inspection of the blower and burner chamber.
  • DZoro
    Is the venturi in perfect condition? No pitting, no scuffing, no chips, no scratches, no black deterioration happening, solid does not move in the aluminum housing? That is a very precise instrument and it needs to be in perfect condition.