Hot Water Unit Heater- How to wire for Instant Off?
NTL1991
Member Posts: 108
I installed a small Beacon-Morris unit heater in my father's basement workshop/garage a couple years back, and it's worked out great on those chilly days and keeps their field stone basement nice and warm. It was a very simple setup at first, with only a mechanical strap-on Aquastat. After some research, I decided on upgrading the Aquastat to a Ranco Electronic temperature control, which works much, much better and is much more flexible.
The only complaint I'm getting from my father is: "It keeps running after I turn the thermostat off and blows cold air!" I've explained that the fan will turn off automatically when the pipe cools sufficiently and that it's not actually "cold air."
Is there a simple way to give me some "Instant-Off" functionality using the existing White-Rodgers thermostat? Maybe with a small RIBU1C or similar relay to cut the small 120V fan in and out with the 24v thermostat? Would this plain jane stat be powerful enough to trigger the Zone Sentry and a RIBU1C together?
Thanks Guys,
Nick
Thanks Guys,
Nick
I didn't think about using the end switch, that sounds like it would work perfectly. Thank you0
This.Zman said:I think I would use the end switch on the taco valves to enable the RIB controlling the fan.
Consulting-1 -
The problem about enabling the fan as soon as the thermostat calls, is that it will be blowing cold air until the water flowing through it gets hot. Not really a problem if the boiler is up to temp and the line is short. Might want to consider putting a timer on the line to delay the fan start a little, and then delay the shutoff to purge some heat.
Rick-1 -
You could wire the rib in series with the present aquastat or snap disk to assure hot water before fan turns on.rick in Alaska said:The problem about enabling the fan as soon as the thermostat calls, is that it will be blowing cold air until the water flowing through it gets hot. Not really a problem if the boiler is up to temp and the line is short. Might want to consider putting a timer on the line to delay the fan start a little, and then delay the shutoff to purge some heat.
Rick"If you can't explain it simply, you don't understand it well enough"
Albert Einstein-1 -
Or perhaps this:
The end switch or "G" closes a RIB sending power to the Ranco.
When the Ranco senses hot water flow it turns the fan on.
When tstat drops zone valve end switch or "G" the RIB is off and fan stops now......no cold air.
You can set the Ranco up to deliver the hottest possible air initially. You could be a hero and make points.
-1 -
JUGHNE, This is exactly the kind of setup I was thinking about.
IIRC, the Ranco's memory is non-volatile, so being unpowered for months at a time shouldn't be a problem. There is a slight startup-delay when the Ranco first powers up, but I think it would be negligible.
Thanks for all the help, guys0
- 117 Geothermal