Vaporstat L408J 1009 life cycle?
Ken Johnson
Member Posts: 29
A little less than 5 years ago I replaced the Pressuretrol on my home single-pipe system with a Vaporstat L408J 1009. It was mounted on an upper port of a Burnham boiler, sharing a siphon loop with the pressure gauge. (The boiler was installed in 1994, before we moved in.) I recently noticed that the cutout pressure was 3.8 lbs, as measured on the gauge, rather than the set 14oz. Cut-in was still 6 oz, as expected. Replaced the Vaporstat, and gauge shows expected cut-in and cut-out.
I replace the thermocouple for the pilot light every two years, after two 'no heat' experiences; one at a very inconvenient time. Should I be planning to replace the Vaporstat every 5 or 4 years in a similar fashion?
Thanks,
Ken
Thanks,
Ken
They should last several hundred thousand cycles (10 to 15 years)(the old mercury ones had a 500,000 cycle mtbf) -- but they can be damaged by over pressure or the port in the bottom may have become blocked.Br. Jamie, osb
Some have failed way before their time without explanation- see this thread:
https://forum.heatinghelp.com/discussion/164305/honeywell-l408j-1009-vaporstat-failuresAll Steamed Up, Inc.
Consulting0
- 110 Chimneys & Flues
- 981 Plumbing
- 387 Solar
- 17 Recall Announcements
